Hi all,
I am installing new 1756-IR6I RTD modules in one of the Controlnet Nodes .
I have a plant down for 20 minutes for this work and put system back in run mode.
Here is the method i think i should follow for this work.please correct me if am wrong any where.
1.Take plc to program mode.
2.Upload plc program and Control net network .save it to hard disk.go offline in networkx.
3.Install the rtd modules .
4.Add rtd modules in PLC program I/O configuration.
5.Downlaod modified PLC program.go offline in RSLogix 5000.
4.Go online with controlnet network (RS networx )
5.Click enable edits,file > save as > optimise and rewrite .(i think here it will download configuration to active controlnet keeper node and allow the newly installed RTD modules to
join the network for communications ).
6.Put the plc back to run mode.
Is there any way to assure that network is configured and all nodes and i/o modules are communicating to controller before taking the controller to run mode.
Please suggest if there is any other better method to do this.
With regards
scan.plc
I am installing new 1756-IR6I RTD modules in one of the Controlnet Nodes .
I have a plant down for 20 minutes for this work and put system back in run mode.
Here is the method i think i should follow for this work.please correct me if am wrong any where.
1.Take plc to program mode.
2.Upload plc program and Control net network .save it to hard disk.go offline in networkx.
3.Install the rtd modules .
4.Add rtd modules in PLC program I/O configuration.
5.Downlaod modified PLC program.go offline in RSLogix 5000.
4.Go online with controlnet network (RS networx )
5.Click enable edits,file > save as > optimise and rewrite .(i think here it will download configuration to active controlnet keeper node and allow the newly installed RTD modules to
join the network for communications ).
6.Put the plc back to run mode.
Is there any way to assure that network is configured and all nodes and i/o modules are communicating to controller before taking the controller to run mode.
Please suggest if there is any other better method to do this.
With regards
scan.plc
Last edited: