1756 MVI configuration

SCAN.PLC

Member
Join Date
Oct 2005
Location
scotland
Posts
53
Hi ,

I am using Prosoft communication module (MVI 56-MCM)MODULE.
I configured the port 1 for Modbus slave with RTU protocol.
Communication link is on RS232C cable connected to DCS via PHONIX CONTACT (serial to fibre optic convertor).
when connected to DCS link my port 1 LED is showing continous GREEEN.BUT DCs serial to fibre converter Tx and Rx are not blinking green ( Tx is blinking green and Rx is blinking Amber).
If data transmission is happening then as per manual it should blink green rapidily.this is for both MVI module and DCS convertor.
Only 3 cables are used in this transmission. transmit , recieve and ground.
RTS & CTS are jumpered.

Also where i should configure the MODULE internal write data block (DCS will read from this addresses) start address.

Also i can see the diffrent offsets for Bits and Integers to be written to internal data block.
How in program that i should tell the module that this is data is bit andthis is Integer.


hope some one can clarify me on this.
 

Similar Topics

Hi , I am using Prosoft communication module (MVI 56-MCM)MODULE. I configured the port 1 for Modbus slave with RTU protocol. Communication link...
Replies
2
Views
6,289
We have a contract to refurbish/upgrade a filling/bottling machine. We have the machine but not its control panel or PLC. We've built a new...
Replies
4
Views
3,898
OK Guys, To set the stage, I have used Channel 0 in User Mode to talk to all sorts of serial devices (mostly PLC5 Family). Now the task is to...
Replies
0
Views
1,703
Hi all I have a ControlLogix 1756-L71SP that i want to use for general PLC applications, not safety. I am running Studio5000 v33, i can't...
Replies
2
Views
49
Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
14
Views
343
Back
Top Bottom