Hi everybody,
I have a strange problem with Siemens EM 231 - 0hcc22 - 0xa0 s7-200s analog input module.
I need to measure 4 analog values. Two of them are pressure and the other two ara temperature.
I have no problem with tempertatures.
The pressure transmitters are siemens 0-10bar 4-20mA. I have to measure the pressure about 1.5 bar and the measurement has to be sensitive. So i measure pressure in the same pipe and take the average.
The problem is when i connect any of the transmitters to AIW2 ,
AIW2 takes 32760 value and in addition to this, other three analog inputs read 4000 more. I will give values definitely to be more clear. transmitters are named trans1 and trans2 , connector of AIW0 is A , connector of AIW2 is B.
1)A is connected to trans1 OR trans2, B is disconnected
AIW0=10560
AIW2=0
AIW4=12150
AIW6=17340
2)A is disconnected , B is connected to trans1 OR trans2
AIW0=4000 ???
AIW2=32760 ??
AIW4=16250 = 12150 + 4100 ?
AIW6=20400 = 17340 + 4060 ?
3)A and B are both disconnected
AIW0=0
AIW2=0
AIW4=12100
AIW6=17200
4)A and B both are connected to any of transmitters
AIW0=14500 = 10560 + 3940
AIW2=32760
AIW4=16000 = 12100 + 3900
AIW6=21100 = 17200 + 3900
As you see, there is no immediate value for AIW2. it is 0 when disconnected and 32760 when connected.
And more strange thing is that , when AIW2 is connected and reading 32760 other three analog inputs read approximetly 4000 more.
i had given 24V DC to the second input directly to make the machine work as a temporary solution and it was remained so for 2 days. i guess i may have damaged the input myself, because 2 days ago i have changed the analog module and transmitters. after changing them , i read normal values from both AIW0 and AIW2.
A stranger thing is that i have changed the old module becasue of the same AIW2 problem.
Analog module is supplied with 24v dc from the smps in the panel and their 0's are same.
Strange problem as you see.. any ideas?
I have a strange problem with Siemens EM 231 - 0hcc22 - 0xa0 s7-200s analog input module.
I need to measure 4 analog values. Two of them are pressure and the other two ara temperature.
I have no problem with tempertatures.
The pressure transmitters are siemens 0-10bar 4-20mA. I have to measure the pressure about 1.5 bar and the measurement has to be sensitive. So i measure pressure in the same pipe and take the average.
The problem is when i connect any of the transmitters to AIW2 ,
AIW2 takes 32760 value and in addition to this, other three analog inputs read 4000 more. I will give values definitely to be more clear. transmitters are named trans1 and trans2 , connector of AIW0 is A , connector of AIW2 is B.
1)A is connected to trans1 OR trans2, B is disconnected
AIW0=10560
AIW2=0
AIW4=12150
AIW6=17340
2)A is disconnected , B is connected to trans1 OR trans2
AIW0=4000 ???
AIW2=32760 ??
AIW4=16250 = 12150 + 4100 ?
AIW6=20400 = 17340 + 4060 ?
3)A and B are both disconnected
AIW0=0
AIW2=0
AIW4=12100
AIW6=17200
4)A and B both are connected to any of transmitters
AIW0=14500 = 10560 + 3940
AIW2=32760
AIW4=16000 = 12100 + 3900
AIW6=21100 = 17200 + 3900
As you see, there is no immediate value for AIW2. it is 0 when disconnected and 32760 when connected.
And more strange thing is that , when AIW2 is connected and reading 32760 other three analog inputs read approximetly 4000 more.
i had given 24V DC to the second input directly to make the machine work as a temporary solution and it was remained so for 2 days. i guess i may have damaged the input myself, because 2 days ago i have changed the analog module and transmitters. after changing them , i read normal values from both AIW0 and AIW2.
A stranger thing is that i have changed the old module becasue of the same AIW2 problem.
Analog module is supplied with 24v dc from the smps in the panel and their 0's are same.
Strange problem as you see.. any ideas?