I have a DCU (from automationdirect) which I have just connected to a 105 cpu, I get a RUN, DIAG and power light on startup. Once I connected the Data light would flash. I am now viewing the file loaded into the plc. I am using DirectSoft32 to make the connection.
GE does not offer manuals for those units anymore but they do have some info. A good tech note on the DCU and GE ONE can be found here:
http://www.gefanuc.com/support/plc/fax01111.htm
Note the section that states:Note the original DCU, the IC610CCM100, does not support the Series One Plus.
There is also a section that explains Switch settings:
The top DIP switch(nearest to the OnLine toggle switch) sets up communications
Code:
Positions 1 and 2 for bits/sec 300 1=Off/2=Off
1200 1=On/2=Off
9600 1=Off/2=On
19200 1=On/2=On
Position 3 for Parity None=Off/Odd=On
Position 4 for OffLine Loopback Disable=Off/Enable=On (Need connector)
Position 5 for TurnAround Delay 0 millisec=Off/10 millisec=On
Position 6 for PowerUp mode Run=Off/Program or Stop=On
Position 7 and 8 Not used
The factory default is all positions Off. A common setting is to close/set On positions 1 and 2 for 19200 bit/sec, no parity. The parity must be None for a modem connection, but may be Odd for a direct computer link. Modems usually also require the 10 millisecond Turn Around delay.
The bottom DIP switch sets the CCM slave DCU ID from 1 to 90. Set positions On or closed to set the binary ID number: close 1 for 1, 2 for 2, 1 and 2 for 3, 3 for 4, 1 and 3 for 5, etc. At least one position must be closed as 0 is not a legal CCM ID number. A common setting is to close position 1 and 2 for an CCM DCU ID address of 3. This ID of 3 is the default for Logicmaster and can also be used for CCM master data collection programs. If you are multidropping more than one DCU/Series One, each DCU must have a different DCU ID.
An EXT/INT power slide switch at the back of the DCU is normally in the INT position to receive power from the Series One power supply. If it is switched to EXT, power for the DCU must be provided at the connector at the side of the DCU using the external cable provided. The connections are White for 0.5 amps at +5 VDC, Green for power ground and Black for Logic Ground. If external power is Not used, the DCU uses 300 mAmp at +5 VDC out of the 1400 mAmp available at +5 VDC from most Series One rack power supplies.
DCU Status Lights and Operation
Since the installed DCU covers up the LED's on the front of the CPU, the DCU provides the same CPU LED's plus an additional DATA LED that is On which data is being transferred from the computer/CCM master. Normally the DIAG and PWN LED's are On and the CPU and BATT LED's are Off, with the RUN LEDS indicating the PLC status and the DATA LED flickering when Logicmaster transferred data.
Detailed LED Status (with Normal marked by an *) is:
Code:
DATA On Data being transferred from/to DCU by Logicmaster/computer
*Off No data transferred or parity/framing error,
invalid header or data or link timeout
DIAG *On Passed DCU powerup diagnotics
Off Failed DCU powerup diagnostics
PWR *On +5 VDC power to PLC and DCU connected
Off +5 VDC power not present in DCU
RUN *On PLC is in Run mode
Off PLC is in Stop mode
BATT On Memory backup Battery has Failed, below ??? volts
*Off Memory backup Battery is OK
CPU On CPU error, check for Enn number with hand held programmer
*Off No CPU error is present
Hope this helps.