4-20mA Calculation

VRBASGRAD

Member
Join Date
Oct 2006
Location
Stoney Creek
Posts
74
I am using Pressure Sensor 4-20mA and at 10 PSI my multimeter is showing me 5,6mA.I just want to know if this is rite, can somebody please tell me how to calculate this.

thx
 
I don't know - what colour is it ?

Seriously , you are asking an open ended question- what you state suggests that this is a 100 PSI transducer
((20-4)/(5.5-4))*10 (I hope I got that right after the beautiful essay posted here about this very subject)

But I could be completely wrong - unless I know two points , I can't extrapolate ( put a line) through your data .
This transducer could be 8-20 PSI , and I would be none the wiser without either you reading what it has stamped on the body , or posting a few more readings .
 
Transducer is from 0 to 100 psi.This is old device; I just want to know if it still works. There is no information except range from 0 to 100 PSI.I want to see at different pressure settings what the output is.
 
well , if you take the span of a 4-20mA signal , you have 16mA , let us divide this 16 into the span of your device (100 PSI) and we should get the ratio :- 100PSI/16mA= 6.25PSI/mA - now you said that your device gave an output of 5.6 mA at 10PSI lets see if this is OK :-

(5.6mA-4mA)*6.25 = 1.6*6.25 = 10

I reckon that is OK then , but you may want to stick a few more PSI up its kilt and make sure that it is reasonably linear .
 
10BaseT. said:
well , if you take the span of a 4-20mA signal , you have 16mA , let us divide this 16 into the span of your device (100 PSI) and we should get the ratio :- 100PSI/16mA= 6.25PSI/mA - now you said that your device gave an output of 5.6 mA at 10PSI lets see if this is OK :-

(5.6mA-4mA)*6.25 = 1.6*6.25 = 10

I reckon that is OK then , but you may want to stick a few more PSI up its kilt and make sure that it is reasonably linear .


Thanks
 

Similar Topics

Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
Replies
5
Views
272
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
Replies
7
Views
275
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
Replies
10
Views
1,683
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
Replies
2
Views
484
Hello this is my first post. Looking forward to being more involved in this community to learn and hopefully help others. Any help or guidance...
Replies
7
Views
785
Back
Top Bottom