Chuck G
Member
This is for an A-B DH+ network with SLC5/04 and KE-1785 modules connecting with a Honeywell DCS.
I've been trying to split a DH+ network with about 25 nodes on it. I took out a small jumper in the middle of the network and place 150 ohm terminators on each new end. After splitting only one side saw all of it's nodes, while the other side only saw the first 4 nodes. After checking all of the conncections on the side that did not come back (per Rockwell's reccomendation), I had to recconnect, and all the nodes came back fine. With all of the nodes hooked together we don't pick up any errors looking at RSLinx.
Other than calling out a Rockwell field tech, I (and my peers) are out of ideas on what to check. Are there any special methods to doing this? The best info I can get says that it shouldn't be a token problem as the lowest number node should generate one.
NOTE: Splitting is required for us because we are adding a new node (another SLC5/04) that is adding 2200 ft+ to the network lenght and we lost half our network when tying it in, so we think we were exceeding the 10K ft limit.
I've been trying to split a DH+ network with about 25 nodes on it. I took out a small jumper in the middle of the network and place 150 ohm terminators on each new end. After splitting only one side saw all of it's nodes, while the other side only saw the first 4 nodes. After checking all of the conncections on the side that did not come back (per Rockwell's reccomendation), I had to recconnect, and all the nodes came back fine. With all of the nodes hooked together we don't pick up any errors looking at RSLinx.
Other than calling out a Rockwell field tech, I (and my peers) are out of ideas on what to check. Are there any special methods to doing this? The best info I can get says that it shouldn't be a token problem as the lowest number node should generate one.
NOTE: Splitting is required for us because we are adding a new node (another SLC5/04) that is adding 2200 ft+ to the network lenght and we lost half our network when tying it in, so we think we were exceeding the 10K ft limit.