hi

I am working with OP7 - DP having IF1 A and IF1B connector I want to connect it to SLC 5/03 I have configured it for IF1A but during download protool is showing the error. I want to know whether this module dose not support to SLC interface? and if it supports how to interface please guide me.

GAJANAN
 
Hi,
What exactly the model of OP7?

If its a OP7 PP - it supports many different manufacturers (Not Siemens)
If its a OP7 DP - it supports MPI/Profibus only (siemens S7)
If its a OP7 DP12 - It supports all listed manufacturers

OP7 DP cannot be used with AB PLC.

Steve
 