data from powerLogic pm9c by mudbus

phinix

Member
Join Date
May 2006
Location
l.a
Posts
33
hi u all,
i am trying to read data from a merlin Gerin powerlogic pm9c
i am using a laptop ,adam 4520 converter(485-322)and a modbus opc server.

i know that the device is transmitting by rs485 modbus rtu and i have configured it to work.
i know that the adam is converting 485 to 232
and i have configured it to work.
i know that the opc server should communicate with the device but it dosn't.

i get a device comunication error on the server

needless to say all baund rates and address are the same.

dear people please help!!!
 
Read pairs of registers starting at an even number

CAN ONLY READ PAIRS OF REGISTERS STARTING AT AN EVEN NUMBER
There is a trap! If You try to read one register you will get an error. If you try to read a pair of registers starting at an odd number (e.g. 1001 and 1002), you will get an error). If you try to read an odd number of registers you will get an error.
 

Similar Topics

Has anyone migrated Proficy Historian data to a new server? I followed the guide to move all the data over, but when I run the utility, it stops...
Replies
0
Views
27
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
7
Views
110
Hi, Wy we log data in PLC using DLG instruction, when we have option to log data in HMI
Replies
1
Views
67
Hi, I cannot find the DLCA1764.EXE utilty software for data retrieving. Can someone share the link to download this software. Thanks!
Replies
4
Views
75
I have an expression in a structured text routine of a Logix controller that looks more or less like the following: ResultInteger := Integer1 *...
Replies
13
Views
371
Back
Top Bottom