PLC 5 online question

bbear

Member
Join Date
Dec 2006
Location
ohio
Posts
63
Hello,

I have used PLC's but I am now working at a site that has PLC 5's which are new to me along with most AB equipment. My question is:
Opening RS Logix5 and opening the current saved program that is running the PLC no problems but when go online is selected the program opens under an old program and it goes online with a version of the program that is active but not correct. Why is this happening and what can I do to prevent it? I do not understand why this is happening I would think it would go online with a current version of the one operating in the PLC without these problems
 
The offline file you are reviewing is not in a directory that is listed in the "Project Files Search Path" in the system Options dialog. When the s/w goes online, it searches the paths specified in that field and trys to match up the processor against the RSP file.
 
Note that when you go online, what you see on the screen is 100% accurate because RSLogix uploads the PLC memory contents. However, the descriptions and comments are not stored in the PLC and may be incorrect.

As jstolaruk said, set your communication path to point to the directory containing your most current offline file, or move the most current offline file to the path that is being used.

If you do the latter, RSLogix will still use the file it thinks is the best match based on the "last edit timestamp" value which is stored in both the PLC5 and the offline file. To get around this, move the file you don't want to go online with out of that directory or delete it. Next, you may see a screen that tells you that a matching file could not be found. It may list files that have the same processor type and name and let you choose one of them, or let you browse to a directory that contains a matching file.

Whatever the case, RSLogix will upload the file when you go online, then you can save it and next time, you won't run into this issue...unless the PLC data or program is altered from a different PC...

Hope this helps,
Paul
 

Similar Topics

Dear all, I am facing an issue at site on a Process PLC (PLC-5) while trying to add 4 new AI channels for Flow Meters. Location is South Sanha...
Replies
2
Views
8,752
Hi. I’m trying to upload program from existing PLC S7-1200. Create new project in TIA v15.1 then upload. After upload successfully, go online but...
Replies
5
Views
218
Sometimes when I am logged in to a PLC and making changes remotely, there's another person using the PLC and making changes as well. Is there any...
Replies
2
Views
839
Kindly, we are trying to go online on an S7-300 plc, with profibus communication, using a CP5711 adapter. But when we open the Ladder and press...
Replies
0
Views
780
I have a device that is communicating to ControlLogix L83E. During apply of online edits to plc, the communication to the device is increasing 4-7...
Replies
3
Views
1,180
Back
Top Bottom