The pump is driven by a 2-pole 45kW motor (notice the 2FX200XG-02/F). It should be fed with a 3-phase 400V supply at 62Hz instead of the standard 50Hz.
A very unusual type of motor!
Make sure you set the base frequency to 62Hz and limit the max frequency to 110Hz, both setpoints should be available on any standard VFD. This way, the VFD will only deliver 400V at 62Hz and up, so you have constant power in the permissable range.
If you're planning on using this pump in the US, you also have to take the different line voltage (440V, or is it 460V?) into account. In this case you also have to limit the base voltage to 400V.