I am trying to get into the basics of that magic no. 27648 & some how not able to decode it:confused:
Here's the problem - I have S7-300 with AI card SM331-7Kf02,12bit resolution. Now the manual says that 12 bit resolution is stored as left-aligned. with LSB's padded with zero.
My understanding is that a 12 bit resolution means 0 to 4095
OR 0FFF Hex. So when I put these in 16 bit format and shift by 3 bits, the number comes to 32767 & not 27648.:confused:
Any one can throw some light on this:wish:

Thanks
 
Siemens uses the values between 27648 and 32767 for over-voltage detection. Where the 27648 value for 100% actually came from is something only Siemens can explain! The difference between 12 Bit, 13 Bit etc. is purely one of resolution - in practice you don't need to worry about it, 100% is always 27648.

You can use FC105 "Scale" from the Standard Library to scale your values to engineering units.
 
All of the Siemens manuals I have referred to show a table giving the values returned for different voltages.
+/-27648 is the nominal range for +/- 100%, however, the unit will still give values up to +117.588% (32511) and down to -117.592% (-32512), anything outside this range gives +32767 or -32768 (this is from an ET200B manual for example)
 
Thanks guys for your inputs. It bugs me why Siemens can't be clear on these information, afterall it's about mathematical calculations only.

Cheers:)
 
It bugs me why Siemens can't be clear on these information
Actually I think this is one of the areas where Siemens is clear, very clear. As "L D[AR2,P#0.0]" says, every I/O module manual I have ever seen from Siemens includes not just one but multiple tables showing how the analogue values are related to signal levels and percentage of full-scale for voltage inputs, current inputs (both with and without 20% offset), thermocouple inputs, RTD inputs, etc etc. It's all abundantly clear. Just unhook your mind from the preconceived ranges of 0 to 4095 and -32768 to +32767, read what it says, and believe it.

Regards

Ken
 
All of the Siemens manuals I have referred to show a table giving the values returned for different voltages.
+/-27648 is the nominal range for +/- 100%, however, the unit will still give values up to +117.588% (32511) and down to -117.592% (-32512), anything outside this range gives +32767 or -32768 (this is from an ET200B manual for example)
We have 4 to 20mA inductive distance-sensors, we measure up to 22mA (these sensors can do this), but we know that the 2mA above the 20mA not a good thing is, not lineair as in the range specified.

Greetz
 

Similar Topics

Hello, I'd like to obtain average of my analog input value which will be displayed on SCADA. For examplle, analog value should be sampled avery...
Replies
2
Views
2,116
Hello, I'm new to siemens and i have problem about analog signals... I'm using a 8x13 Bit AI, a 4x12 bit Ao and a combo 8 bit 4ai/2ao card. How...
Replies
5
Views
6,131
I have a client who has asked for a pop-up for each of their analogs, which will display the alarm values. The values displayed in the pop-up...
Replies
5
Views
2,530
hi i am using s7-300(CPU 313c). when i try to use FC106 unscale function, i can change IN manually but there is no effect on OUT. i wrote PQW752...
Replies
4
Views
1,584
Hi guys, I have CPU S7-300-313C ( Cat No - 6ES7-313-5BE00-0AB0) DI24/DO16 and AI5/AO2. when I am trying to configure and use the AO channel PQW...
Replies
4
Views
2,551
Back
Top Bottom