Out of my head:
The plc's have to be connected to the MPI network. (Hardware configuration properties of the plc. Connected to network must be yes).
All plc's must have unique MPI address. Save and compile all hardware configurations.
In the s7 manager right click on the MPI connection and select define global data. Now you you see the matrix. Add plc's to the coloms. (Click at the top of the first colom, and select add/select plc)
When this is done you can start to define the interface.
Example:
Code:
CPU1 CPU2
DB20.DBW10 DB21.DBW2
DB21.DBW8 DB22.DBW6
A cell in the matrix can be receiving or sending data. In this example it might be that CPU1 is sending DB20.DBW10 and CPU2 is receiving this information in DB21.DBW2
When finished defining the matrix you have to compile it. (Compile twice, in the right bottom corner of the screen you will see phase 1 after compiling the first time and phase 2 after compiling the second time. When compiling twice (phase 2) then the configuration is stored in the SDB and on eprom/flash memory card) Then download this global data definition to all plc's using the download button in this configurator.
We use puls bits in all plc's to check wether the connection is still "alive".