Does anyone have any experience bringing in OMNI flow totalizers values into a AB PLC-5?

I am trying to get data from a bank of 7 OMNI 6000 flow computers using a Prosoft MCM-3100 installed in a AB PLC-5/20. This is Modbus communication via serial cable. 32 bit float data, flow/temp/pressure etc, look good but the totalizer values are not correct and do not resemble anything close. In the OMNI the totalizer data is 32 bit long int. The Prosoft module is master the omni the slave and the PLC gets the data via Block Transfer (BTR) commands. Prosoft module has data storage of 4000 16 bit words (0-3999) so the totalizer value would be stored in word 0 & 1. How can I get those two words brought into the plc with the correct values?

I have searched this board and was wondering if this is what needs to be done:

http://www.plctalk.net/qanda/showthread.php?t=16051&highlight=32+bit+long+integer

If so could someone enlighten me a bit on why this happens

Thanks
 
LA,

You must use the same "language" at each data transfer point, or if not possible, you must convert the data from one type to another. The Omni is talking with 32-bit signed Long Integer words (no decimal point, no fractional parts). Make sure that you are using the Long Integer format for transferring the data at each step. Long Integer data will not directly transfer correctly to a Floating Point data file. Note that the PLC 5/20 does not have the Long Integer data type available. Your choices are to either convert the data to single 16-bit Integer (N file type) numbers, or convert it to the Floating Point (F file type).

Here are the data file type descriptions from RSLogix:

F8 - Floating Point This file stores a # with a range of -3.40282347e38 to -1.1754944e-38 and 1.1754944e-38 to 3.40282347e38. F8 is the default file number. For this file type, you can assign any file number from 3 thru 999. This file can be 1,000 float words (32-bit words) maximum.

L(3-4095)
Long Used to provide a 32-bit signed integer. Each L file can contain a maximum of 4096 elements. 2 words/element. The L file type cannot be used in an indirect address. (Available only with the SoftLogix 5 controller)
Rockwell Software Inc., 1997, 1998, 1999, 2000
 
Last edited:

Similar Topics

Hi, So we have a flowmeter installed but doesnt have a feature to send a pulse to plc for it to compute the total volume. I want to somehow...
Replies
3
Views
574
How is it going y'all? So We have had a pesky problem with an EH 300 flow meter. We are using EIP to reset the totalizer, and for some reason the...
Replies
3
Views
788
Good morning, I have a flow meter that has an output pulse configured to 378.541 liters per pulse. My question is, do I just count the pulse per...
Replies
19
Views
1,800
Good morning, I have a flow meter that that has an output with is a pulse. The pulse is configured to 378.541 liters per pulse. My question is...
Replies
6
Views
701
Hello You guys helped me with a similar issue some time back on storing totalized values to different tags each month. I have a similar issue...
Replies
19
Views
1,492
Back
Top Bottom