Hi,


I have 2 inputs in the PLC for decrease and increase the motorspeed.

The drive MM440 is connected on profibus to a s7-315-2DP master.

In the control word I have bit 13 and 14 to use the MOP (motorized Potentiometer).

SHould I use these bits or should I make MOP in the PLC and use the setpoint in the PZD

Wich one is the fastest and the best ?
 
Combo said:
Hi,


I have 2 inputs in the PLC for decrease and increase the motorspeed.

The drive MM440 is connected on profibus to a s7-315-2DP master.

In the control word I have bit 13 and 14 to use the MOP (motorized Potentiometer).

SHould I use these bits or should I make MOP in the PLC and use the setpoint in the PZD

Wich one is the fastest and the best ?
hi....
i think its better u go for the control word bits than going for plc.
its faster and u dont need any logic to be developed for that.. and also u save 2 "VALUABLE" outputs in the PLC since, there is no other factors to be considered...

sueksh
 
but if you do it in the plc, it is more flexible (easy change of limits and steps,...).
i think it depends on your machine, if it is complicated then i would go for plc ladder programming...
 
Problem with the MOP speed setting

fvsds.JPG


So I have 2 buttons connected on a PLC, the inputs are interconnected to the MOP Up and the MOP DOWN via profibus...

Problem is that there is a ramp before the setpoint of minimum 2s.

When they want to set a speed setting (the drive gives it's actual speed to a display), it's very difficult to say, let's regulate to 20 m/min.

So, now I have the troubles because of using MOP...

I will trey now via PZD.
 
I would suggest using PP04

This will give you (from PLC-->Drive):
Word 0, Control Bits
Word 1, Speed Ref +/- 200%
Word 2~Word5 User Defined

From Drive~PLC:
Word 0, Status Bits
Word 1, Actual Speed+/- 200%
Word 2~Word5 User Defined

Don't mop via I/O...if you must right directly to value...not via Up/Down. If your using MOP local on drive just switch between Data Sets.

Nick
 

Similar Topics

We have a mm440 drive that is not starting remotely in automatic. We can control the locally when in hand mode with 0-10v potentiometer. When we...
Replies
5
Views
1,370
Hi all, i m new to this forum. i recently had an assignment where the user wanted to copy parameters from Siemens Micromaster 440 using BOP. Help...
Replies
3
Views
5,782
Hi, I'm using PPO1 to communicate with MM440. I only need to read and modify MM440 parameters, so i sucssesfully use PKW mechanism. I don't have...
Replies
1
Views
1,304
Dear all, Could you please help me a bit? Please check the attached pictures. PIW582 is the signal from the MM440. Act. Filtered torque. In the...
Replies
2
Views
1,486
Sir, I have Siemens mm440 drive .which is using for conveyors .it's speed is controlling through pot (analog input 0-10 volt) But i am facing...
Replies
44
Views
11,300
Back
Top Bottom