I'm not sure if valve is the right name in english,

If u have a double working cilinder, the you cannot use 3/2 and need 4/2 valve, or 5/3.

When do u use 4/2 and when 5/3 ?

Is 5/3 good for emergency stops ? I mean, when their is such a stop, the compressed air is cut and u don't want to have a motion anywhere ?

And 4/2 for general applictaions then ...


Just for updating my pneumatic knowledge
 
Is 5/3 good for emergency stops ? I mean, when their is such a stop, the compressed air is cut and u don't want to have a motion anywhere ?
For such an application, it is not enough to cut the supply air. Be sure that the air on the output side is vented in the inactive (middle position).
 
Originally posted by JesperMP:

For such an application, it is not enough to cut the supply air. Be sure that the air on the output side is vented in the inactive (middle position).


...unless such an action will increase the level of the hazard. Your hazard assessment should be able to tell you that. I have had cases in the past where an all ports blocked center position was deemed a safer option than center exhaust.

But, then again, (for those of you in the US) I am finding I am NOT smarter than a 5th grader. So take my responses for what they are worth.

Keith
 

Similar Topics

I have an actuator operating a clamp that requires PLd/SIL3, I’ve seen some SMC double valves with feedback, but they are described as dump...
Replies
9
Views
2,331
So how do you go about controlling the open center or open center valves? To get to that closed or open part, I assume you need to have both...
Replies
21
Views
4,139
What are the differences among solenoid valve, solenoid air pilot valve and air pilot valve? I read a powerpoint slide from a website (Please see...
Replies
3
Views
1,360
It has come to my attention that the old PLC-2 system was Tric outputs so it did not matter. We have a Micrologix 1400 PLC with add on I/O modules...
Replies
28
Views
8,573
Any thoughts on this one? I'm designing the controls for an operator-loaded, light-guard protected hydro-pneumatic press (pneum approach...
Replies
3
Views
4,364
Back
Top Bottom