SLC5/02 communications problem

Terry Boblitt

Member
Join Date
Jan 2006
Location
Willisburg, Ky.
Posts
119
New guy 1st post so be easy..Yesterday I Installed a 550 panelview(2711-K5A2)tied to a slc 5/02. Today I made some changes(to the 5/02)--no problem. Later on tried to go on line it seemed to try then it said communications failed retry or go offline. Went to another machine and tried and everything worked--ok.The panelview is working flawless with the slc. I can't go on line.I'm using a PCMK card with a 1784-PVM4/B cable. Could the processer be the issue even though it working fine?
Thanks to all
 
1)restart your processor first

2) can you see processor on rslinx if yes
there should be no problem to go on line with PLC.
 
When you downloaded your changes, did you by accident, change your comm port setup?

I've done that before, and if you happen to click accept too quickly and miss the "apply communication changes" dialouge box and don't go online afterwards, you could miss it.
 

Similar Topics

Hi there, I have 3x SLC 5/04 processors communicating with each other over DH+. Some external equipment is being replaced and a new packaged...
Replies
4
Views
2,249
I am using the 9300 usbs convertor to connect to a SLC5/04 on channel 0. with 1770-kf2/1785-ke/scanport device on rslinx lite 2.43. initially I...
Replies
5
Views
2,671
I need to program an Allen Bradley SLC5/05 processor to read and write data to/from an ABB (Alfa Laval) PLC. Do I use the MSG (message) block or...
Replies
18
Views
10,567
Hello there, Recently I have had to change the ethernet router in my system. The old system worked fine but the new router has a different set of...
Replies
6
Views
2,988
Hello everyone. I think I am doing this right. My question to all is: Is it possible to convert a slc5/01 to communicate with rsview32 over a...
Replies
3
Views
2,357
Back
Top Bottom