Hi,

I'm new to software redundancy. I have two 315 2DP Cpu's that should connect to two IM 153-2's. I have 8 I/O modules that I would like to place next to the two IM153-2's on the same rack. But is this possible? Now I have IM|IM|DI|DI|DO|DO|AI|AI|AI|AO, but only the second IM is running well, the first IM in the rack goes into failure.
I can't find much on the siemens website, maybe I'm looking in the wrong places?

Thanks for helping!
Hendrik
 
Do you use the special active backplanes for this and the special couplemodule for the IM cards (or IM redundancy bundle).
Otherwise the hardware config is not exactly the same. Copy the complete racks from cpu a to cpu b in the hardware config. One minor difference between both gives trouble.
Also check your program, or is the profibus not running from cpu B not running?
There is a small doc format manual delivered with the software redundancy software or from siemens.com. Very important is to do the redundancy programming within the OB35 call in the program, as described.
If you change the settings (in/out) of the special function blocks, delete online the 3 generated datablocks before putting the cpu back into run. These datablocks are generated automatically when starting the software redundant cpu for the first time.
 
Last edited:

Similar Topics

I'll preface this by saying this is the first time I've worked on a Siemens system and I'm fairly unfamiliar with them. I might mess up some of...
Replies
29
Views
728
Hi We were having a few power cuts and the CPU would not work. I had to reset the memory and he CPU would read from the memory card and start...
Replies
13
Views
3,153
Dear Sirs, I had a problem with CP 343-1 with CPU315-2DP.I had newly add the CP343-1 Ethernet module to the hardware to allow me to access this...
Replies
5
Views
2,626
Hello Experts I have a little problem in dealing with addresses. I am using a profibus absolute encoder Hengstler make. This encoder is spec2:64...
Replies
11
Views
4,348
Hi All, One of our clients wants to replace some obsolete VFD's on their plant. There are two S7-315-2DP plc's and drives are connected via...
Replies
2
Views
3,428
Back
Top Bottom