Member
Join Date
Feb 2005
Location
Grand Rapids, MI
Posts
1,322
Cross posted from Mr.PLC.com

Anybody have any experience with the E5AR temperature controller on DeviceNet?

I have a customer trying to connect this to an AB 1747-SDN scanner (master). Have not been sucessful keeping communications working, scanner faults with a 77 error (basically data size mismatch). This is with the default parameters. Per Omron tech support we have the most recent EDS file.

Default parameters will not work for the application and when they try to modify the parameters, typically the scanner will not even find the controller.

Any suggestions would be appreciated.
 
When you have a connection data size mismatch, you have to resolve it from both sides.

How many bytes Input and Output data are configured for the E5AR's scanlist entry in RSNetworx for DeviceNet ?

I am not familiar with the E5AR. Can you tell me how much data it expects to exchange with a scanner under the default I/O connection ?

If you have the ability to get RSNetworx to run the "Class Instance Attribute Editor", you can read the expected I/O connection sizes from Class 05 (DeviceNet Connection), Instance 02 (Polled Connection), Attributes 7 (Produced bytes) and 8 (Consumed Bytes).
 
Ken,

Thanks for the input. The customer will be checking that information in the morning. There is a bit of learning curve for both parties on this project.

Your help is appreciated!
 

Similar Topics

Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
2
Views
26
Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
Replies
4
Views
99
Hi dear . I have a system with cj1m cpu11 etn. previously NT 5z HMI was connected with plc. recently my old HMI got damaged. I want to replace it...
Replies
7
Views
118
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
56
I am working on a project using a NB screen and NX1P2 PLC. I am having a really hard time getting a real number to properly translate through to...
Replies
3
Views
116
Back
Top Bottom