Beijers E1000 - Modicon Modbus Master

Philg

Member
Join Date
Jul 2006
Location
Adelaide
Posts
14
I am trying to set up a E1101 to be a Modbus master to a Deep Sea Electronics 5220 controller. The DSE5220 has a RS485 connection.

At the moment I am using a Modbus Slave Simulator to simulate the DSE5220 (download from http://www.modbustools.com/ )but are finding that I get a lot of "1:Comm err stn 10" messages on the E1101 even though the data is being updated across the Modbus connection.

There is no handshaking and the Baud Rate is 9600, 8,n,1 so pretty standard.

Other than the RTU Silent Time under the General settings tab in the driver I can't see too much to adjust to help with data collisions.

I have been sniffing the communication with LookRS232 and the data is below. Where a line status error ocurs the comms. locks which seems to be causing the error on the screen... anyone got any ideas ???

0572.438<0A 03 02 00 4E 9D B1
0572.344<0A 03 00 00 00 01 85 71
0569.953<0A 03 02 00 4E 9D B1
0569.875<0A 03 00 00 00 01 85 71
0569.391<0A 03 02 00 4E 9D B1
0568.969<0A 03 00 00 00 01 85 71
0567.094<01 00 01 85 71
0567.063|A line-status error occurred
0566.563<0A 03 02 00 4E 9D B1
0566.438<0A 03 00 00 00 01 85 71
0564.000<0A 83 03 70 F3
0563.953<0A 03 02 00 4E 9D B1
0563.657<0A 03 00 00 00 01 85 71
0563.157<0A 03 02 00 4E 9D B1
0563.078<0A 03 00 00 00 01 85 71
0562.578<0A 03 02 00 4E 9D B1
0562.500<0A 03 00 00 00 01 85 71
0561.985<0A 03 02 00 4E 9D B1
0561.922<0A 03 00 00 00 01 85 71
0559.969<80 00 01 85 71
0559.953|A line-status error occurred
0559.453<0A 03 02 00 4E 9D B1
0559.391<0A 03 00 00 00 01 85 71
0552.985<20 00 00 01 85 71
0552.969|A line-status error occurred
0552.485<0A 03 02 00 4E 9D B1


NOTE:
0A 03 00 00 00 01 85 71 is the string from the Master
0A 03 02 00 4E 9D B1 is the reply from the Slave
 
I believe the problem was being caused by having two controllers connected, one to each comm port. As one driver wasn't connected to a device when it faulted it stopped the comms of the other driver !!! this is what was causing the line status error.
 

Similar Topics

Hello, Does anyone have any experience of using a small label printer with a Beijers E1000 Series HMI. I haven't decided on a particular model of...
Replies
2
Views
4,218
I currently have a E1101 talking across Modbus to a DSE 5220 Genset Controller using the following driver… Com1 – modicon Master/Modbus Naster...
Replies
3
Views
6,977
I am using an E1101 Beijers HMI touch screen HMI/GUI in conjunction with an FX3 PLC. The E-Designer software is version 7. The Alarms screen 990...
Replies
3
Views
4,364
Is anyone aware of whether you can access the FTP data (trend backup data) through the PPP connection ? I connect using the PPP connection, and...
Replies
3
Views
3,225
I have two Trend graphs but only want to back one of them up to the Compact Flash card. Under "System Settings\Commands" according to the manual...
Replies
2
Views
4,338
Back
Top Bottom