BitHammer Member B Join Date Mar 2007 Location Chicago area Posts 2 Mar 21, 2007 #1 I can't get a PLC Direct DL06 to respond via serial link. The RX1 light flashes, but the TX1 does not. Is there any way to hard reset this beast? Thanks.
I can't get a PLC Direct DL06 to respond via serial link. The RX1 light flashes, but the TX1 does not. Is there any way to hard reset this beast? Thanks.
s7xp.com Member Join Date Jan 2007 Location Rotterdam Posts 151 Mar 21, 2007 #2 Only a software reset. Do you have the correct cable. The RS232 requires a jumper between rts and cts. Otherwise a protocol or address failure. Use the auto detect function of Directsoft.
Only a software reset. Do you have the correct cable. The RS232 requires a jumper between rts and cts. Otherwise a protocol or address failure. Use the auto detect function of Directsoft.
BitHammer Member OP B Join Date Mar 2007 Location Chicago area Posts 2 Mar 23, 2007 #3 Got it! Thank you for the response. The problem was the driver for the USB serial port adapter. I did find out the hard way about RTS/CTS jump, though!
Got it! Thank you for the response. The problem was the driver for the USB serial port adapter. I did find out the hard way about RTS/CTS jump, though!