A month or so ago I posted a topic about using 460volt 60hz
motors on a 400volt 50hz supply. The application is a hydraulic pump that applies pressure via a beam with cylinders that extend the beam to squeeze product together. The consensus
was that since the motors were running at 50 hz, the motor rpm would not be at rated value, and that max power output could not be reached. So, the process might suffer.
My thought was that since available connected voltage
was actually only 395 phase-to-phase, is that under load the motor would draw more current at max load than it was rated at.
Well, at high pressure settings on the hydraulic system, the pump/motor makes an ungodly noise and about 25% of the time trips the breaker that feeds its starter/overload. The breaker is a 15 amp rated unit, the motor nameplate says 9.2 amps max at 460volt.
My question (finally! ) is this: Would putting a drive on the motor and programming it to output 460v 60 hz supply help this situation any? At lighter loads, the unit presses ok, but when more pressure/larger loads of product to be pressed are needed, the pump/motor seems to be straining.
motors on a 400volt 50hz supply. The application is a hydraulic pump that applies pressure via a beam with cylinders that extend the beam to squeeze product together. The consensus
was that since the motors were running at 50 hz, the motor rpm would not be at rated value, and that max power output could not be reached. So, the process might suffer.
My thought was that since available connected voltage
was actually only 395 phase-to-phase, is that under load the motor would draw more current at max load than it was rated at.
Well, at high pressure settings on the hydraulic system, the pump/motor makes an ungodly noise and about 25% of the time trips the breaker that feeds its starter/overload. The breaker is a 15 amp rated unit, the motor nameplate says 9.2 amps max at 460volt.
My question (finally! ) is this: Would putting a drive on the motor and programming it to output 460v 60 hz supply help this situation any? At lighter loads, the unit presses ok, but when more pressure/larger loads of product to be pressed are needed, the pump/motor seems to be straining.