Ab 1200

Leon

Member
Join Date
Mar 2007
Location
Ohio
Posts
75
I have an older AB 1200 Series A that is in the Run mode, and I can not download a new program. Does anyone know how to clear the memory or program? I have auto configed and the path node is OK.

Thanks
 
There should be key switch on the back of the unit that puts the PV into program mode. It used the same key that works on the PLC5s
 
1200

Yes I am talking about a 1200 PLC and not a PanelView

Thanks for the reply guys.
 
Have you made a connection with RSLinx, if so can you upload program?
Once you upload program then go online, put processor in the program mode. Then click on comms and click clear memory.
 
Thanks

Thanks Mickey as that did work. 3 AB people in town here where I get my materials and support did not know how to do it or they just didn't want to tell me. Now I can use it for any project.

Leon
 
Whoops

Mickey,

I have a series C and that series A on the the same rack. I made a mistake and did that with the series C and it did clear it and I did have to download again. After I realized that I tried the same thing with the Series A. When I try to go to comm in RSLinx all I get is the RED X over the processor and then I am stuck with a no communication error to the processor and the path and node are correct.

Sorry about that, but I was in a hurry and haste makes waste.

Leon
 
Okay, so let's resolve whether you can connect to the MicroLogix 1200 Series A controller at all.

MicroLogix 1200 controllers have a "Communications Default" button on them, right below the trim pots near the Channel 0 serial port plug. When you press this button and the "DCOMM" LED is lit, the Channel 0 serial port will be set to the default configuration of DF1 Full Duplex at 19200 baud.

When in the DCOMM mode, connect your PC and use the Autoconfig feature in the RSLinx DF1 Full Duplex driver setup. If this works, then you'll be able to clear the controller memory or download to the controller.
 

Similar Topics

Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
Replies
4
Views
111
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
Replies
0
Views
80
Hi, I have a 1214 on ip 192.168.0.100. This is connected to other modules through a switch on same network. I need to connect this to a company...
Replies
1
Views
140
Hi. I’m trying to upload program from existing PLC S7-1200. Create new project in TIA v15.1 then upload. After upload successfully, go online but...
Replies
5
Views
198
Hi all, I am trying to do Modbus communications via the CB1241 RS485 Communication Board on a Siemens S71200 PLC. I am using a 1215C CPU. After...
Replies
6
Views
229
Back
Top Bottom