A-B SLC 5/04--Any Hope?

cntrlfrk

Member
Join Date
Feb 2006
Location
Nebraska
Posts
244
Walked in to a SLC5/04 that seems to be dead. It continuously flashes the lights similar to a power-up self test, pauses, then repeats.

I can't communicate via DH+. I've cycle power, pulled it, pulled the battery, re-installed with no luck.

New processor seemed to do the trick.

Are there any 'tricks' other than what I mentioned above, or is this just junk?
 
Have you reset the 504 to factory settings ?

Whats the flashing, if you look in the manual i am sure the different blinks mean something..!
 
There was really no light blinking sequence to follow in the chart. Like I said, it was pretty much like it was repeating the initial power-up sequence...Fault light, then DH+ light, then all lights, then DH+ light...pause...repeat.

However I've never done the 'short GND to Vbb', and that seems to have done the trick. Wonder how many have been tossed without trying that??

Thanks guys.
 
cntrlfrk said:
There was really no light blinking sequence to follow in the chart. Like I said, it was pretty much like it was repeating the initial power-up sequence...Fault light, then DH+ light, then all lights, then DH+ light...pause...repeat.

However I've never done the 'short GND to Vbb', and that seems to have done the trick. Wonder how many have been tossed without trying that??

Thanks guys.

Loads ! , the cap keeps a charge for ages .
 
Same thing happened to me once.
In fact the SLC 5/04 was fine until the power was cycled.
It came up showing no communication on DH+ and processor fault.
We ended up changing the processor.


Kim
 

Similar Topics

I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
51
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
65
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
93
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
91
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
Replies
0
Views
74
Back
Top Bottom