You could try to do this but I don't know that you want to.
A plc isn't going to be fast enough to directly control the trigger point of an SCR. You won't be able to correctly sync to the AC line. At the very least you will need to use a solid state phase control relay. This will allow you to send an analog signal from the plc to control firing angle.
However, unless you want to run the risk of burning up your motor, you will also need some current limit method. This will require another analog input to your plc so you can limit the desired firing angle based on motor current.
As for speed control, you could use either armature voltage feedback, a DC tachometer or an encoder. No matter what you use you will need yet ANOTHER analog input or counter card and will need to further modify your firing angle to achieve the speed you desire.
You will probably also want a phase angle feed forward structure to get your phase angle reasonably close to what you need based on speed command before any control elements are even required.
This all assumes that your plc scan time will be fast enough to give you the speed control bandwidth you want AND (even more of a stretch) that the analog inputs and outputs on your plc are fast enough to get the information to/from the physical system as quickly as you need to.
Or you can forget all that and, as Leadfoot said, get an adjustable speed drive. This unit would contain the SCRs, the pulse firing logic, the speed control, the current limits and the enable control. All you would do from the plc is send an analog signal proportional to the desired speed to the drive and the drive will do the rest. And these things are pretty cheap.
Keith