In the RSLogix500 Help File for the IOM instruction it says:

Note: Expansion I/O is not permitted with the IOM instruction.

What is their definition of Expansion I/O in the ML1200? I have a SLC 5/04 that uses IOM on Analog Output cards that are within slots on the local rack.

But for the ML1200, are cards such as the 1762-OW16 treated different? Are these considered Expansion I/O?
 
An ML12000 comes with either 24 or 40 built in I/O. This is based on the catalog number (1762-L24 for 24 or 1762-L40 for 40) that you have.

Anything beyond that is considered expansion I/O. I believe you can hook up to 6 (six) expansion I/O modules.

So yes, the 1762-OW16 is considered expansion I/O.

Hope this helps.
 

Similar Topics

Hey all! Long time reader, first time poster! I have an EA9-T7CL and an MicroLogix 1200 connected via DF1. I'm all good and got everything mostly...
Replies
3
Views
628
Hi every master,Recently i met a fault about 1762-L40BWA 1,When i get the PLC, The Fault light is lighting, I am not remember the fault message,I...
Replies
0
Views
707
Hello everybody and master,I met a problem about ML1200.It is described as below: 1,When i got this PLC,The FAULT light is lighting, My computer...
Replies
4
Views
1,075
I had planned to use PTO instructions to control a servo motor, single axis only. We have a ML1200 BWA model. According to the ML1200 manual...
Replies
7
Views
3,436
I am using Modbus to read 36 registers from a ML1200. 2 of those registers are suppose to be L11 data and 2 of the registers are F8 data. Long...
Replies
3
Views
1,362
Back
Top Bottom