We have an Allen Bradley 505 processor connected to a Panelview using the RS 232 cable configured for DH 485. I would like to connect the ethernet port from my laptop to the ethernet port on the 505 so I do not need to disconnect the Panelview cable when I go on line to the processor. Any Ideas on how to configure the ethernet channel 1 on the processor. Hardware address, Subnet Mask, gateway address etc. and/or if I could be directed to a comprehesive pdf. file on the subject.

Thanks
Leviathan
 
First, you need a cross over cable or switch
Second, you need to know the IP on your laptop.
Then, connect to the PLC. Open rslinx bootp (no IP on the slc to start with by default)
Enter 255.255.255.0 for the subnet on the bootp
Wait for the bootp message from the plc
Assign it a IP address. Click disable bootp to assign it
Open linx. Add the ethernet devices.
Configure the driver, add the node for the ip you assigned to the plc
Now you should see it on Linx.
Goto logix, system comms, pick the plc, go online.

matt
 
This article shows you how to add the node and drivers to linx. Which you will need to do. However, the first part uses serial to set the ip and such, and the whole point is not to use serial here.

If the slc has never had ethernet used on it, then it has no ip, and bootp is enabled. There isnt anyway to set the ethernet that I know of short of using bootp, or using the serial first.

If you dont mind using serial one more time, and you can connect to it with dh485, then it is easier to set the ethernet that way.
 

Similar Topics

Hi, I have been trying to run drive via Sysmac studio. I can ping the drive. I can see the logic bits going on/off as per command. But, drive is...
Replies
20
Views
318
Hello. I am trying to use a Prosoft AN-X4 to improve the communications for a new panelview plus 7. This is going from a SLC-500 through DH+ to a...
Replies
5
Views
127
I'm retrofitting equipment, but I didn't want to change the electrical characteristics of the panel. In this equipment I have a dedicated...
Replies
0
Views
55
I've got a Micrologix 1100 with ethernet and I'm trying to configure communications to a Fanuc R30iB controller. I'm pretty sure you have to set...
Replies
0
Views
76
Hello, I've been trying to learn this a while now and still have not found out how this works. I have an Omron CJ2M PLC and an ABB ACS 355 VFD...
Replies
1
Views
175
Back
Top Bottom