Smar FB/I transmitter

pulsar55

Member
Join Date
Jun 2006
Location
NY
Posts
6
We have a Contrologix plc with Foundation Fieldbus instruments and a CN2FF linking device with Smar I/FB transmitters which are working very well . We also have Smar FB/I transmitters which do not work at all . We are using National Instruments Fieldbus Configurator 3.1.1 . Has anyone had any sucess with the FB/I transmitters . There is no support from National Instruments with there software , Smar has been very helpful ,Rockwell has not been much help . We have other Fieldbus instruments which are working fine . If anyone has any suggestions they would be much appreciated we are getting desperate .
Thanks
 
Last edited:
Could you elaborate on "do not work at all" ?

Post more details about what device you're using, how you have configured it, and what is not working as you expect.
 
Smar FB/I

The device in question is Smar FB/I 302 with a 4-20 ma output for a 0-100% pump speed . We are using them for pump pacing on different skids . They have a bad data quality in the Analog function block .Also the transducer block shows a output failure in the Diagnostics tab . The I/FB 302 units which feed back pump speeds to the plc work just fine . We have changed the firmware revision according to Smar to make them compatable with the CN2FF linking device , ver.3.45 . Any insight would help
 

Similar Topics

Hey guys, I've a pilot plant that are controlled with Smar instruments with Fieldbus standard. I'm going to control the plant by S7-300 (PID...
Replies
9
Views
2,218
We recently replaced a Siemens 505 with RSLogix 5000. Our boiler is controlled by CD600 Smar for pid loops. They are still being used for the...
Replies
0
Views
2,225
We have enough Hart transmitters to warrant getting Siemens' PDM software to configure and keep track of xmtr configurations. PDM uses a Hart...
Replies
0
Views
3,696
Can I use PanelView 550T with PLC SMAR LC700. I suggest usign modbus, but how really connect it. I mean do I need addition modul on PLC or just...
Replies
1
Views
2,497
I need to protect some pressure transmitters from hot (120°C) oil. Does anyone have a favorite transmitter cooling element/standoff they use...
Replies
4
Views
146
Back