will a slc 5/04 read an input switch that has a 10V drop?

produktion

Member
Join Date
Mar 2007
Location
MI
Posts
19
I have to reuse some equipment and the switches on the equipment is using Namco switches. EE230-304-20 is one of the switches. I have found that these are 20-230V AC/DC switches with a 10V drop. That drop is for both AC and DC.

Will this cause issues with the AB processor?

Thanks
 
What voltage input module are you going to be hooking it too.

When you say a 10 volt drop do you mean that if you put 110VAC in you get 100VAC out and if you put 24VDC in you get 14VDC out?
 
TWControls said:
What voltage input module are you going to be hooking it too.

When you say a 10 volt drop do you mean that if you put 110VAC in you get 100VAC out and if you put 24VDC in you get 14VDC out?

Yes, that is the concern I have exactly.
 
TWControls said:
Which module are you going to hook it too? What voltage are you wanting to use?

1746 IB16 input modules. These are currently in use and will not be able to be changed. They are wanting to reuse the Nemco switches and REALLY avoid having to replace them.
 

Similar Topics

I have a site with SLC505. The analog card is working but the ladder program is not sensing any analog inputs. It will be helpful if any one can...
Replies
6
Views
5,186
Hello, is it possible to read a message using a controllogix L61, from a SLC, that is connected to a PLC-5 that already is sending data to the...
Replies
7
Views
2,084
Hello, I inherited a control system one of my predecessors thought it was a good idea to put logic for cant optimization and Kinetix motion...
Replies
15
Views
3,411
Hello. I have a new 5069 L320ER that I installed and I am trying to read and write data to an existing SLC5/05 via Ethernet. They are both on the...
Replies
4
Views
2,498
Hello, I have a PID block in my program controlling pump speed in order to get a correct Differential pressure. The way I have it set up is the...
Replies
3
Views
1,232
Back
Top Bottom