two panelview600's one micrologix 1500, possible ?

GTX

Member
Join Date
Dec 2003
Posts
36
Hello All,

I have a micrologix 1500 PLC and two Panelview600's both DH-485 (2711-T6C5L1 ser.A v4.2).

I was wondering if it is possible to hook both of them up to a micrologix 1500, so one would be in Channel 0 and one would be in Channel 1.

Is it possible ? How is it done ?

Thanks for any input !
 
Yes,
You could configure both ports for DH485.
Or use one port configured for DH485 and network ML1500 and both PV's together( preferred method IMHO). See PDF's
 
DH-485 is a network type infrastructure. It can support up to 32 devices.

You would therefore only need to tie up a single channel on the MLX 1500 and set it for DH-485. Each device would have a unique node address which would be a decimal between 0 and 31.

Hope this helps.
 
Thanks everyone i will try this next week when i am back at work and let you know how i make out.
 

Similar Topics

I have been asked to upload an old/existing program from an obsolete PanelView600, using Panel Builder32 software, and dump it in another 600. I...
Replies
8
Views
2,063
Does anyone know how to have the Panelview 600 write its internal time in seconds to a register in a PLC5/40 I want to create a monitor in the...
Replies
0
Views
1,099
Gentlemen, It happened so, that one of two PV600 was stollen. I have a picture of rear label from the second PV, and I know that both of PV had...
Replies
12
Views
4,924
A Micrologix 1400 has been replaced. It had the same program loaded in it after it was installed. There are 2 panelview 600's that now won't...
Replies
1
Views
1,302
Hello I have a problem with Gauge Indicator. When the value is changed, it disappears scale and numeric value. Does anyone know what is wrong...
Replies
5
Views
1,828
Back
Top Bottom