We having a problem with a Thermo coupler input card, on a SLC500 PLC.
Keep lossing coms with the signals.. Have checked everything that I can think of....
The plant may operate for several weeks without problems and then shuts down.

Once the PLC is reset, everything operates well for a while or several weeks.. any ideas ???

Thanks
 
Assuming this card is a 1746-nt4 or nt8.
What exactly happens. Do the lights for each channel go out or do they blink?
If you can go on-line with the processor look at the configuration files (the input Files) for the slot that the card is in . That will set up all of the parameters for each channel. The manual is on AB's site.

My guess is that a certain sequence of events writes over what should be there. When that happens you will lose the readings from the card.

When you reset the proc. There is probably an instruction that sets all of those parameters . So The card is fine again for a little while.


Drewcrew6
 
Last edited:
Loss of communications?

Are you actually getting a loss of communication?

It sounds more like you have a Block Transfer Read instruction that stopped functioning.
By resetting the PLC you re-initiate the BTR and the problem clears up until next time.

Monitor that particular BTR and see if it is the culprit.
You may need to use a timer to re-initiate the BTR, when it fails, until you can find the real problem.

Let us know.
Roger
 
Sorry I have not had time to go to site personally and see exactly what is actually going on...... As soon as I have any more details I will post another message...

sorry

Paul
 

Similar Topics

Hi, I am working with a L35E and a Yaskawa VFD using Ethernet coms. I use AB's Generic Ethernet Module to communicate. Is there a Tag that I can...
Replies
3
Views
1,744
Dear team, We are constantly facing M07 incremental loss on one of our kinetix 6500 safe torque. We have changed Servo motor (MPL-B4530K-MJ72AA)...
Replies
1
Views
101
Hi folks ! Got an older Modicom BM85 and I suspect that it's not passing data to ModBus+ network. We had a power loss for a few days and I suspect...
Replies
0
Views
66
Communication between devices will stop working for a certain period of time. I caught the error message using WireShark. I cannot identify the...
Replies
0
Views
98
The client has an application that when communication between the PLC and the Factory Talk VIEW supervisory fails, the object in the supervisory...
Replies
5
Views
277
Back
Top Bottom