hi,
just i want to know, how to create alarm msg of the cpu which is gone fault
assume we have active powersupply, cpu and io cards and redundant powersupply, cpu and io cards
usually if active cpu some fault occurs, the process is taken by the redundant
but wan to know how can we create a msg that in active cpu some fault as occured, so that we can replace it

thanks
 
Hello anusri;

the answer will be diferent depending on the family of PLCs you are working with: Controllogix, SLC500, PLC5... Also indicate what redundancy module you are using for your application.
Please specify.
Hope this helps,
Daniel Chartier
 
there is a status file in some AB plcs which have a bit which goes HIGH to indicate CPU / IO fault... but u have to give more details about ur PLC config for a specific answer....
 

Similar Topics

Hi guys, I have no experience when working with AllenBradley PLC, but I hope someone could clarify the result of multiplication shown in the...
Replies
14
Views
2,190
Hello everyone! Posting from Argentina as I don't know what else to do. For a bit of context, I am using an Allen-Bradley Micro850 PLC and five...
Replies
16
Views
10,430
Hi, I want to communicate slc5/03 cpu with Delta tp04 hmi through rs232 port. I tried through 1747cp3 cable directly but can not communicate...
Replies
0
Views
932
Hi there, I have an application where I’m required to connect Siemens S7-300 PLC (Profinet) to Allen Bradley Control Logix Remote I/O Rack &...
Replies
11
Views
3,653
Dear all, Can any one share the procedure how to configure Allenbradley PLC as modbus TCP server with DCS through Prosoft PLX31 EIP MBTCP
Replies
1
Views
2,160
Back
Top Bottom