Consider a resistance-heating load comprised of 12 heaters. Each individual heater is rated for 3000 watts at 480 volts, 3 phase and all the heaters are located approximately 25 feet from the enclosure containing the switching device. Is it permissible to run a single set of appropriately sized (6 gauge) conductors, fused at 50 amps, across the 25 feet and then tie all the individual heater leads to these conductors at a power distribution block. Do I properly understand NFPA 79 article 7.2.11.2 (quoted below) to mean that additional fusing of the individual heaters is not required, despite their relatively small gauge lead wires? Thoughts? Anything else that could necessitate additional fusing?
---
Quoted from the 2002 edition of NPFA 79.
7.2.11 Resistance Heating Branch-Circuit Overcurrent Protection.
7.2.11.1 If the branch circuit supplies a single non-motor operated load rated at 16.7 amperes or more, the overcurrent evice rating shall not exceed 150 percent of the load rating.
7.2.11.2 Equipment employing resistance-type heating elements rated at more than 48 amperes shall have the heating elements subdivided. Each subdivided load shall not exceed 48 amperes and shall be protected at not more than 60 amperes.
7.2.11.3 The addional overcurrent protective devices shall include all of the following:
(1) Installed within or on the machinery or provided as a separate assembly
(2) Accessible but need not be readily accessible
(3) Suitable for branch-circuit protection.
The main conductors supplying these overcurrent protective devices shall be considered branch-circuit conductors.
---
Quoted from the 2002 edition of NPFA 79.
7.2.11 Resistance Heating Branch-Circuit Overcurrent Protection.
7.2.11.1 If the branch circuit supplies a single non-motor operated load rated at 16.7 amperes or more, the overcurrent evice rating shall not exceed 150 percent of the load rating.
7.2.11.2 Equipment employing resistance-type heating elements rated at more than 48 amperes shall have the heating elements subdivided. Each subdivided load shall not exceed 48 amperes and shall be protected at not more than 60 amperes.
7.2.11.3 The addional overcurrent protective devices shall include all of the following:
(1) Installed within or on the machinery or provided as a separate assembly
(2) Accessible but need not be readily accessible
(3) Suitable for branch-circuit protection.
The main conductors supplying these overcurrent protective devices shall be considered branch-circuit conductors.