Dear All,
I need to interface fire detector (Smoke, Flame , manual call point, sounder, solenoid and beacon etc) with Allen Bradley Control Logix PLC.
The detector at customer sites are Apollo make ionisation smoke detectors and Thorn make flame detector (IR type)
Problems:
These detectors when in normal state(safe state - no fire) they draw very less current (in micro amps) and in alarm state(fire) they draw something around 55milli Amps.
We need to detect fire state( = 55mA), Open circuit(0 amp or infinite resitance), short circuit(0 resistance)
How to interface smoke and flame detectors with AB CLX AI card which can read a maximum of 20mA(safe state).
Now how to design circuits(resistance etc) to use the normal AB AI card to read for open, short and fire condition.
Smoke and flame detectors give analog current.
Manual call points are digital. with manual call point we have to detect manual call point activated and open circuit (short circuit if possible as short and activation are same result)
The other issue is to find for open, short with sounders, solenoid and beacons(these are digital outputs)
The above smoke, flame, manual call points are inputs to PLC (Smoke, flame Analog input and Manual call point(digital input)
As with detecting open,short and fire condition with input signal we also have to detect for open, short circuit for solenoids, sounders and beacon. as these circuit will be off most of the time and only in case of fire it will be energised. for safety we need to monitor for open and short in solenoid or sounder or beacon and report that as a fault signal.
So each of these detectors and outputs has an End of line resistance to indicate for open circuit.
Has any one interfaced smoke,flame,beacon, sounder and solenoids.
If yes can u please tell me how to design the circuit with end of line resistance etc to get the conditioned signal to normal AI and DI card.
I thought of using AB CLX diagnostic input module and output module to detect for Open and shorts with Digital Signal. But there is no such diagnostic cards for AB Controllogix(CLX) AI card.
can you please share your experience.
Because i could not get much details from Apollo or thorn(Tyco) website.
I hope there will be some fire engineer(specialist) in this field.
thanks
I need to interface fire detector (Smoke, Flame , manual call point, sounder, solenoid and beacon etc) with Allen Bradley Control Logix PLC.
The detector at customer sites are Apollo make ionisation smoke detectors and Thorn make flame detector (IR type)
Problems:
These detectors when in normal state(safe state - no fire) they draw very less current (in micro amps) and in alarm state(fire) they draw something around 55milli Amps.
We need to detect fire state( = 55mA), Open circuit(0 amp or infinite resitance), short circuit(0 resistance)
How to interface smoke and flame detectors with AB CLX AI card which can read a maximum of 20mA(safe state).
Now how to design circuits(resistance etc) to use the normal AB AI card to read for open, short and fire condition.
Smoke and flame detectors give analog current.
Manual call points are digital. with manual call point we have to detect manual call point activated and open circuit (short circuit if possible as short and activation are same result)
The other issue is to find for open, short with sounders, solenoid and beacons(these are digital outputs)
The above smoke, flame, manual call points are inputs to PLC (Smoke, flame Analog input and Manual call point(digital input)
As with detecting open,short and fire condition with input signal we also have to detect for open, short circuit for solenoids, sounders and beacon. as these circuit will be off most of the time and only in case of fire it will be energised. for safety we need to monitor for open and short in solenoid or sounder or beacon and report that as a fault signal.
So each of these detectors and outputs has an End of line resistance to indicate for open circuit.
Has any one interfaced smoke,flame,beacon, sounder and solenoids.
If yes can u please tell me how to design the circuit with end of line resistance etc to get the conditioned signal to normal AI and DI card.
I thought of using AB CLX diagnostic input module and output module to detect for Open and shorts with Digital Signal. But there is no such diagnostic cards for AB Controllogix(CLX) AI card.
can you please share your experience.
Because i could not get much details from Apollo or thorn(Tyco) website.
I hope there will be some fire engineer(specialist) in this field.
thanks