I need to periodically trigger 2 outputs at certain encoder value.
Siemens advices us to use a FM350-1 to do this.


For example:



When the actual count value (ACT_CNTV)=2000àtrigger DQ0

When the actual count value (ACT_CNTV)=5000àtrigger DQ1 AND reset the encoder value to start all over again.







The triggering of the two FM350-1 outputs is no problem, but my question is: how can I reset the encoder value, without lose of pulses.





A second question is that when I write a value to CMP_V1 or CMP_V2 (new comparator value) I expects to read this value in ACT_CMP1 and ACT_CMP2, but these variables stay 0.



Thank for your advice

Leonardo
 
In many cases you don't actually need to use the embedded inputs and outputs with its rather complicated setup. Get the counter value directly from the process image and use it together with an offset value. Never mind reseting the raw value in the counter module.



Example:
Address of the FM350-1 is 272..287. Then the raw count value (ACT_CNTV) is found in PID276.



Reserve a DINT for a UserCount value and another DINT for ZeroOffset value. On reset signal, the counter raw value PID276 is moved to ZeroOffset. This is performed in a single scan, on positive edge of the reset signal.



Reset:
A Reset
FP OneShotHelp
JNB END
L PID 276
T ZeroOffset
END: NOP 0
The UserCount updates in every scan:
L PID276
L ZeroOffset
-D
T UserCount
It's easier to make your own limit values with simple comparator (Greater than and/or Less Than) in the program, rather than the more complicatet procedure for evaluating the counter modules own limit values.
 
hi. thanks for your help about this problem. i have another question about hardware. how u configuration it for run? and take it as the manual direct. but it can't run, can you teach me more. thank your help
 

Similar Topics

We are currently encountering configuration problem with FM350-2 used for counting and totalizing functions. When we configure the FM350-2 and...
Replies
1
Views
3,173
i have problem with siemens fm 350 counter module on a s7-300. the "cr" lamp is off all the time, and the lamp "dir" always on... so the counter...
Replies
0
Views
4,114
For a revamp we will have a configuration with S7 1500 and FM350 in ET200M on profinet. Will the FM350 work? Because I see in Siemens Tia...
Replies
2
Views
2,718
Hi All, First time I have ever worked with encoders and I am having a slight issue. The encoder is set up counts up and down and works well for...
Replies
2
Views
2,030
Hi Once again need your help.Looking for information about module FM350. We observed sometimes the module is counting negative value starting...
Replies
2
Views
1,955
Back
Top Bottom