Hi all,

I met a problem with my PVP setting, "global connection can not start", during I run HMIs. and I lost all of signals from SLC CPU.

but I can test application with my RSView Studio. I don't know what's wrong.

and I can not configure RSlinx Enterprise setting in my HMI terminal setting.

could you guys please tell me what can I do for it?

thanks in advance.

mars
 
Did you create a communications path in both the "Local" and "Target" tabs? If you were able to test your application on the PC, you must have set up the "Local" tab.

If you have not already done so, create the same communications path in the "Target" tab.

If you have already configured the "Target" tab, try re-downloading your application to the terminal. When you do, make sure to "Replace Communications."

Hope one of these suggestions works for you...
 
rgurin said:
If you have already configured the "Target" tab, try re-downloading your application to the terminal. When you do, make sure to "Replace Communications."

Hope one of these suggestions works for you...

this is worked, thanks a lot.
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
76
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
53
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
77
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
Replies
0
Views
89
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
129
Back
Top Bottom