Can any of you offer some insight to selection of an electric or pneumatic actuator for ON/OFF ball valve? The valves will need to be FAIL LAST STATE and both elec and air are readily available. What should be the deciding factors? Is pneu more reliable? Is elec more costly?
 
I generally prefer electric. Pneumatics can be cheaper IF you already have the compressor, drier, filter, etc. Frost can be a problem for outdoor mounted pneumatics. It used to be that you could get more precise control with pneumatics, but that's not generally the case now.
 
Electric actuation is more expensive and generally much slower.

As pointed out above, electric actuation is more controllable and precise. Electric actuation is also probably more suited for temperature extremes like outdoor applications.
 
To have the "FAIL LAST STATE" condition, a motorized electric ball valve would be the best way to go... if you loose your OPEN and/or CLOSE signal to the valve it will remain in the last state it was in. To get the same operation in a pneumatic valve you need a air to open, air to close which is generally more expensive than the spring to close or open versions. Electric actuated gets more expensive when you try to have fail to close operation because you require a sensing circuit and battery pack to provide power to close or open the valve
 
Precise positioning?

Since the valve to be controlled is a quarter turn ball valve the only desirable states are OPEN and CLOSED. Ball valves are not used for throttling flow. This eliminates the "precise positioning" part of the discussion.

If plant air is available and the actuator will not be in a location prone to freezing, the pneumatic seems to me to be the better option. Even with a double acting actuator I believe it would be less expensive than the equivelant motor operator.
 
When selecting your FAIL LAST STATE/POSITION actuator, have a look at the newer type of actuator that does not require external solenoids to hold position upon air or signal loss. I have found that with the cost of the standard actuator plus the fail safe solenoids, is greater than a newer type actuator that has this function internally.

I replaced SMC IP6100 type actuators with the fail safe extras for the new IP7100 digital model at lesser cost.

The change out was a result of the failsafe relays/solenoids failing when exposed to heavy rain.
 

Similar Topics

Per title - what's the worst and best wire duct brands you have worked with, and why? They all look the same on the outside, but there are...
Replies
13
Views
2,392
I have installed a Cognex barcode scanner on a machine. I have a 1769-L18ER CompactLogix processor. I have communication setup and working. I...
Replies
26
Views
4,546
Is there anyway to be certain that the memory module in a ML1400 has been written to with the current program? I have controllers in the field...
Replies
0
Views
867
Hello all, I'm trying to come up with an elegant solution to check an Array of Values to see if they are greater than zero but less than 15 My...
Replies
11
Views
2,347
Hello experts; If i want to compare two companies PLC's features which points should be considered especially if i want to compare Siemens and...
Replies
9
Views
2,477
Back
Top Bottom