Analoge signals

osamamalhy

Member
Join Date
Jan 2006
Location
alex
Posts
89
Hello Every one
i have siemens analoge signal module that could be connected to 0 :10 volt or 4: 20 mA also it can be connected to pt100 , i had a pt100 ,2 wire , i like some one to tell me how to connect it to the plc , cause i had try bur just had no thing,,,,kindly help
osama
 
Hello osama;

First thing, I suggest you download the manual "S7-300_Module data" from the Siemens support website, it has a chapter that covers in detaiol the procedures for analog sensor connections and configuration.

Next, here is a brief list of things to do to connect your RTD and read values in the PLC:
1) configure the module in the HardwareConfig editor; select the channel you will connect to, the type of sensor and other parameters.
This will give you 2important informations: the input address for the channel you are configuring, and the position of the measuring range module. This measuring range module is a square jumper, marked A,B,C and D along its sides. You must position the module so the correct letter (as indicated in the hardware configuration) is lined up with the marking arrow. this will ensure the input card reads the correct voltage levels.
Measuring_Range.jpg


2) connect the 2-wire sensor as described in the manual I suggested, or on the accompanying diagram for your module (if it is new, it was in the box). Here is a general connexion diagram for 2-wire RTD sensor:
Two_wire_RTD_SM331.jpg


The exact pin numbers to connect to will vary depending on the module model you are using.

3) download the configuration to the CPU, and (for example)use the FC105 "Scale" function to read and scale the PIWxxx address you were given in the HardwareConfig editor for the channel you want to read.

Note that the above mentionned manual will also explain the analog value representation scheme for Siemens S7 PLCs.

Hope this helps,
Daniel Chartier
 

Similar Topics

I have a question reaguarding analoge signals in CJ1M. When using 4-20mA / 1-5V the value in the program is &0 - &4000 If I want to use a 2-10V...
Replies
1
Views
1,457
I have a omron cj1m-11cpu with: 3x cj1w-id211 (16 inputs) 3x cjiw-od212 (16 outputs) and a mad42 (2 anologe outputs 4 analoge in puts) I wrote a...
Replies
1
Views
1,794
Hi gentlemen Is it possible to force an analoge value in these CPU before 400 what i notice is i cannot write PIW128 in force table to force it...
Replies
4
Views
3,040
I am Trying to make the analoge output of the expansion module follow the oppisite of the analoge input on the device. So, when I have 0 volts on...
Replies
2
Views
2,081
Hello every one.. How can I mov analoge data come from 1756-IF16..in RSLogix5000??? I used mov instruction source (Local:8:i.ch0data)and dest...
Replies
4
Views
4,781
Back
Top Bottom