1756-OB Configuration

Mark Aldrich

Member
Join Date
Jul 2007
Location
Utah
Posts
4
I am trying to set up a ControlLogix PLC and the output cards (OB16 and OB32) both have a blinking OK light. The manual tells me to configure the module. What do I need to do?
 
Local or remote rack?

For local rack, download a program that includes the module in the I/O config, and put it in run mode.

For remote racks, download a network schedule if needed (ControlNet, EthernetIP I/O, etc).

Blinking usually indicates that the module is okay, but has no active communications connections to a processor.

What state does RSLogix5000 show the module in, in the I/O tree while Online? Check the module status there.
 
In addition to what was said above any output will have blinking OK if controller is not in RUN mode.


Any yellow triangles in I/O configuration?
 
Contr_Conn said:
This bit is for DeviceNet scanner only, I assume he is using 1756-OB modules, so it has nothign to do with scanner

D'oh! You're right, as usual I'm opening mouth and inserting foot! That's what I get for assuming and replying to a post after talking to someone about remote racks!
 
Summary: The original problem was that the output modules showed the OK light blinking in green and the documentation stated this meant the module needed to be configured. The actual problem was that the PLC was not in the "run" mode, therefore the outputs were not being updated. Once the PLC was put in the "run" mode, the OK light became steady and the outputs became active.
 

Similar Topics

Hi Guys, I am doing a project that involves a Ring Configuration with 1756-EN2TR with Field Fiber Device 1783-ETAP2F and 1783-ETAP1F. I am not...
Replies
12
Views
2,108
Hiii, I want to communicate MGate MB3180 to my ML1400 channel0 configuration as my ML1400 as Modbus RTU master. But i need pin configuration for...
Replies
4
Views
1,742
Anyone has an experienced configuring 1756-CFM module for Contact Output that triggered by overspeed alarm ? This CFM module was to monitor engine...
Replies
0
Views
1,892
Hello I have problem on RSLogix 5000 v20 project IO configuration. I can't see 1756-EN2TR/C rev 10 when adding new module or by discover modules...
Replies
0
Views
1,865
Dear All, I have problem with configuring the 1756-CFM in RSLogix5000 Version 19, this module is used to monitor Engine Speed thru the Magnetic...
Replies
6
Views
4,545
Back
Top Bottom