RMA said:
The multi-meter in current mode is effectively a short circuit compared with the 0.7V or so voltage drop across the diode. THe voltage drop across the meter will be in the mV region, so the current takes the path of least resistance and flows entirely through the meter.
Of course! Thanks for reminding me of what I should have learned (hah!) 35+ years ago in Electronics 101 when studying these devices.
rsdoran said:
I am assuming a PLC is involved, if so when the incoming analog values are out of range an alarm light could be turned on. If an HMI is involved the value could be displayed.
The simple solution may be to add an analog or digital panel meter but may cost $50 or more per panel, if multiple analog signals are involved this could get expensive.
You have assumed correctly about the PLC in the most recent application. This project that what brought the question to mind was an unusual one for us that had (18) analog inputs and (2) analog outputs. there were (7) different types of devices, some self powered and some where the loop power had to be provided.
I really don't like the idea of disconnecting and reconnecting wires to check the loop current, so I thought that maybe we should just build in testing points as a standard when we have these kinds of applications.
Just as a point of infomation the circuit that caused us the most problems was a loop between an analog level transmitter, about 100' from the plant, and a analog input module. We knew we had a full tank and that we had to get some type of reading from the transmitter, but weren't. Used my cheapy signal generator that I bought from Grainger (9V w/4-12-24mA output selections) to validate that we (that is the contractor) had wired everything correctly. Utimately the problem was due to lack of a correctly "wetted" signal, or should I say a mis-wiring of the voltage source.
This brings up another question that I have resolved for myself, but I am always interested in the opinions offered here:
Scaling this many signals from Data Units to Engineering Units. Depending on the PLC being used, I may have diffent options for scaling. Some have scaling parameters (like SCP in RSLogix 500, or XYFS in Idec), many don't (RSLogix 5000, Misubishi GX Developer) so I have to write a scaling routine based on information that I obtained on this site. Usually I have an operator interface available. I currently have adopted the setting of analog conversions through the interface (using data registers), not through an on-board scaling function like Mitsubishi's Beijer units have, or scaling that can be performed when progamming the analog module) rather than hard coding the conversion values into the program. Regardless of the number of analog I/O signals. Any thoughts?
... rab