can you help me implemetning the logic showed as ladder rung in the following picture?
logic1.jpg

I need to realize it with classical and timer relays.
Can you give me any suggestions?
Thanks
 
Because, I want my circuit to behave like that. I want whole circuit to be in Run mode only when there is a transition of start signal from 0 to 1. in other words I want stop contact to break circuit even if start is still pressed and to start again when start is releasd and pressed again i.e. when there is a positive edge.
 
hi there

Two push buttons one with NO element(for starting motor) and other with NC element(for stopping the motor) and a contactor of appropriate amps size will do.
Do search for DOL CIRCUIT in Google.
 
mikas_m said:
Hello,
can you help me implemetning the logic showed as ladder rung in the following picture?
logic1.jpg

I need to realize it with classical and timer relays.
Can you give me any suggestions?
Thanks

Hardwired with relay (starter) this if fairly straightforward.

When hardwired the Stop pushbutton is normally closed i.e. the power goes thru it to the start button; therefore if Stop is pushed then Start can not do anything.
http://www.patchn.com/motors.htm

This is a standard, 100 years old or more, motor control ckt.

BTW, there would be no need for a one-shot for this when programming a plc. ALSO, the STOP button should be N.O. in the code BUT the physical switch should be normally closed.
 
Last edited:
I suppose it is a great idea

you can use a timer of 0.5 sec or less as follow:
start . . . . . . . . . . . . . . timer
--] [-------------------------------( )---

start . timer . . . . stop . . . . .Run
--] [----]/[-----------]/[----------( )---
. Run . . . . .|
--] [----------|
 
Last edited:
Well, this is not for the motor. I made this looks simalr to get a lot of ideas. Basically, start is relay contact from elswhere which can "start" some other logic. I want to use "stop" as NC pushbutton (when user press, it breaks connection) to some kind of "acknowledge", so to end "run" even if condition to start is still present. i have currently implemented this exactly like sinanissa. Timer is more expensive component, but I guess it is necessary.
Thank you all for your suggestions.
 
HI,
I think it's a good circuit to prevent the operators from jamming a screwdriver or pocket kinfe into the start push button & walking away. Do you need this circuit hard wired, or programmed? There are hardwaer timers available that have a one shot function. When the timer input goes true even for a brief period, their output contacts will close for an adjustable amount of time. When that time expires, the contacts will open. The timer won't close the contacts again until there is a false to true transition on it's input. In ladder logic you may want to use a timer triggered by the start button, then use the timer timing bit for a start --| |-- in the next rung.
BD
 
My circuit is supposed to be hard wired and I have only classical relays. I guess I'll need to buy timer. can you suggest something cheap?
Thanks
 
Don't need a timer


start.JPG





For the life of me I can't see why you would want this though, what's wrong with the good old fashioned way, where you have a spring return pushbutton.
 
I should have read the explanation of why you wanted it...


also my mistake :oops:


the link up to R1 should be between the Start and the N/C R1 contact, no after the R1 contact.

Therefore once pressed and R2 comes in, R1 retains until the start is released.
 
You can tell its a long time since I designed hardwired circuits

start2.JPG



As well as moving the connection for the R1 coil, should also add a n/c R2 contact otherwise R1 would go mad.
 
Solved

PeterW said:
You can tell its a long time since I designed hardwired circuits
As well as moving the connection for the R1 coil, should also add a n/c R2 contact otherwise R1 would go mad.

Thank you Peter, it is exactly what I want. I'll implement the way you suggest.
I knew this forum is the right place to ask question.
 
Peter - depending on the structure of the contacts for R2 this may not work. Standard relays will unmake one set of contacts before making the opposite set. The NC contat from R2 may unmake before the NO can make sealing the circuit. I think you'll just have a buzzer.
 

Similar Topics

G
respected sir,i want ur help,, i got 4 floor model of an elevator,,,with 4 cabinet-call push buttons on each floor,,the problem i m facing is,,,i...
Replies
5
Views
2,302
Ze Blind Pig
Z
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
Replies
9
Views
110
Hello, I am trying to replicate a piece of logic on the PLC5 onto an SEL RTAC. I am using ladder on SEL and FBD. I am having issue on the ladder...
Replies
9
Views
109
I'm fairly new to Rockwell software, I've had some basic training in the past but nothing too advanced. My company and I use Reliable products for...
Replies
11
Views
332
Back
Top Bottom