Dear friends,
Presently we are commissioning S7-200 CPU 226 based machine in our soap plant. The configuration is CPU 226 + EM235 + EM232 + EM 231.
EM 231 is the last module attached to PLC. The problem is 24V LED of this module is not glowing & this module is inactive. I have checked 24 V at connector, it is there. In all other connected modules 24 V LED is glowing. When I powerup PLC for once SF LED ( Red ) glows for a sec & then switches off.
On further checking I observed that there are 8 nos. DIP switches on this module & all are in OFF position. In EM235 ( module next to CPU) there are 6nos of DIP switches & switch no.1 & 6 are ON rest are OFF. Is this got any connection with non glowing of 24 V LED on EM 231 or the module has become faulty & needed to be changed.
Kindly advice
Regards,
Neeraj
 
Hello neeraj;

If you have 24 V DC at the L+/M contacts and no LED, then either you have blown a fuse (solid-state fuse, on the circuit board) or your module is shot.

You can confirm this status by reading SMB12 and 13: these are Module ID (SMB12) and Error code (SMB13) for module 2 (3rd IO module on the bus).
Here are they can be decoded:

S7_200_IO_SMB.jpg


The dipswitches are used to configure the input channels of the analog module:

S7_200_EM231Dispsw.jpg


Hope this helps,
Daniel Chartier
 
Last edited:
I wish I could see the registers but I dont have the software to go online. The supplier has already couriered the new module from Italy but the only thing bugging me is why all the DIP switched are off.
 

Similar Topics

Hello Friends, I am beginner in Siemens PLC programming. Can anybody guide me do we have Tech Support Help(Chat Or Call) for Siemens PLC(S7...
Replies
2
Views
2,748
hi, i am installing GSD file with API field value as 0 & downloading project & it is working fine but , when i try to install same GSD file with...
Replies
0
Views
2,030
hello, All LED's on Siemens PLC(CPU 315-2 PN/DP)are blinking continiously & program is not getting downloaded in PLC.i try to format MMC card but...
Replies
10
Views
8,851
Hello, I want to communicate with Siemens S7-300F PLC.The CPU Model is 315F-2DP and CP Model is CP341.But i do not know what protocol it...
Replies
2
Views
1,662
The HARDWARE: S7-226, Microwin (will possibly upgrade to version 4, from current 3.2), HMI (Maple systems) with a Parallel port, attached to a...
Replies
0
Views
1,535
Back
Top Bottom