Dear friends,
Presently we are commissioning S7-200 CPU 226 based machine in our soap plant. The configuration is CPU 226 + EM235 + EM232 + EM 231.
EM 231 is the last module attached to PLC. The problem is 24V LED of this module is not glowing & this module is inactive. I have checked 24 V at connector, it is there. In all other connected modules 24 V LED is glowing. When I powerup PLC for once SF LED ( Red ) glows for a sec & then switches off.
On further checking I observed that there are 8 nos. DIP switches on this module & all are in OFF position. In EM235 ( module next to CPU) there are 6nos of DIP switches & switch no.1 & 6 are ON rest are OFF. Is this got any connection with non glowing of 24 V LED on EM 231 or the module has become faulty & needed to be changed.
Kindly advice
Regards,
Neeraj
Presently we are commissioning S7-200 CPU 226 based machine in our soap plant. The configuration is CPU 226 + EM235 + EM232 + EM 231.
EM 231 is the last module attached to PLC. The problem is 24V LED of this module is not glowing & this module is inactive. I have checked 24 V at connector, it is there. In all other connected modules 24 V LED is glowing. When I powerup PLC for once SF LED ( Red ) glows for a sec & then switches off.
On further checking I observed that there are 8 nos. DIP switches on this module & all are in OFF position. In EM235 ( module next to CPU) there are 6nos of DIP switches & switch no.1 & 6 are ON rest are OFF. Is this got any connection with non glowing of 24 V LED on EM 231 or the module has become faulty & needed to be changed.