I am working on a project that has a SLC 500 with two racks of remote I/O. I am upgrading to C-Logix and would like to remove the SLC processor and Remote I/O.
Any suggestions of a network module that could be added into the SLC chassis? I would prefer to use E-Net.

Thanks Rich
 
This is a conversation I've had a lot of times with A-B marketing reps, and the short answer is that the only protocol that's compatible with both ControlLogix and the 1746 I/O system is A-B Universal Remote I/O (RIO).

You can put a 1756-DHRIO in scanner mode in your ControlLogix chassis, and use 1747-ASB adapters on the SLC chassis.

Although the 1747-ACNR adapter can also control an entire SLC chassis, it is not compatible with the 1756-CNB(R) bridges for the ControlLogix.

There are no plans that I know about for A-B to build an EtherNet/IP adapter for the 1746 or 1771 series of I/O chassis.
 
I’ve used remote I/O on another project and it worked ok. Was hoping to avoid it this time one would think with their push to use E-net they would have a better solution. But guess NOT!
 
rkukl said:
I am working on a project that has a SLC 500 with two racks of remote I/O. I am upgrading to C-Logix and would like to remove the SLC processor and Remote I/O.
Any suggestions of a network module that could be added into the SLC chassis? I would prefer to use E-Net.

Thanks Rich

How about using ControlNet using the 1747-ACN15 in each 1747 Rack
 
OkiePC said:
ControlLogix 1756-CNB cannot control SLC i/o this way. A PLC-5 with C-Net can, however.

Thanks for straighting me out, I just checked the available communications devices and the 1747-ACN is not there
 

Similar Topics

Hello all! I have some machines that run an SLC 5/03 and occasionally a fault is generated. Recent Example: A power supply wasn't screwed in...
Replies
3
Views
421
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
Replies
7
Views
553
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
Replies
23
Views
2,592
Machine has existing DN devices that are connected to SLC 5/04. All communication is working fine now. Supplier wants to remove some DN devices...
Replies
6
Views
841
I'm having a strange issue where the operator can input a desired speed in 0-110%, and the scaling will correctly translate that in Hertz to the...
Replies
6
Views
2,285
Back
Top Bottom