icon10.gif
how can i program or make an arrange to manipulate 20 or more pid´s in siemens s-7, remember a thread of NICK B & KEN M but dont understand at all, can i make an acumulator on ob35? for trigger pid´s individual?

ROGER
icon10.gif
 
Hello shade;

In one project we did 25 temperature loops in a S7-313C-2DP processor, all in OB35, set at 100ms. Of course the rest of the program was as compact as we could make it (we used the available technological functions to control heating SCRs), and we used multi-instance DBs to limit the amount of memory we needed to process the whole project. But the OB35 call was not a problem.
Your main limitation will be the work memory available on your CPU, not the cyclic OBs.
Hope this helps,
Daniel Chartier
 
thanxs for your reply D.Chartier
icon10.gif


all at the same time? ill need to check the specifications of your cpu vs mine, im using a cpu 417-4h. ill try for trigger the pid´s at diferent times, i dont know if 2 or 4 at a time will be fine.

kensuke.jpg
 
A 417 is a lot of Horsepower...and thus would not worry about it. You have a lot of Interrupt OB's (OB30~38). On a small 300 with only OB35 to play with I would probably build a mux and break the calls into 4 to keep the jitter done.

Nick
 
As Nick B says, "A 417 is a lot of Horsepower!"

When setting up your timed interrupts for processing you PID loops, bear in mind the process. There is no point running your PID loops faster than the the feedback is likely to change. i.e. a temporature control loop will run acceptably at a relatively low update time but a position control loop would want to run much faster!

Nick
 
icon10.gif
thanx nick´s!!

is great to know that
icon17.gif
i´m using a filter level control, for a gas refinery. think i need low update 500ms 1sec maybe.
so if i do a 24 pids with this proccesor, Nick you think i need to make interrupts???
icon10.gif


if yes
can you please give me some small explanation how can i do that any example will be great.

else
just for curiosity, can you please give me some small explanation how can i do that any example will be great.

////////////THANX!!!!!
icon10.gif


end.

kensuke.jpg
 
icon9.gif
damn i have troubles, i can make one of the pids work fine, but i cannot make 2 work simultaneously, or switch them, there only works the first one, the second stays into zeros.

does any one have any solution????

i know, it must be simple, but i cant see the answer, i need my 23th coffee cup,
icon10.gif
 
Timed interrupt OBs are configured in the hardware config for the processor and are executed at a regular interval e.g. OB35 every 100mS.

If you post the code the doesn't work for you, someone may be able to offer advice on what's wrong with it.

Nick
 
icon10.gif
SORRY MY MISTAKE
icon17.gif


I´m using a 412-1 for tests right now, cuse the 417-4h is on instalation, alrready manipulate 3 pid into ob35, they don´t worked cuse i dont toggle the setpoint input, when i toggle the inputs they start to work! is that normal??? isn´t COM_RST that for¡???

kensuke.jpg
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
6
Views
118
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
134
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
297
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
109
Hi everyone hope you'll well. Is it possible for me to download a Crack version of tia portal v13..sorry to say this but the software is very...
Replies
5
Views
198
Back
Top Bottom