We have 2 robot welding cells in the rear of our plant that have just started getting Watchdog timeout faults on the SLC 5/05 CPU's.

"0022: The User Watchdog scan time has been exceeded. In the processor under the Data Files S2 - Status, Scan Times, the following is labeled:
Maximum = the highest scan time recorded, I believe this only resets if you download a new program x1, not sure though it might reset when you go from pro to run.

Average = the average scan time recorded x1

Watchdog = the limit that is set to trigger the error x10"

These cells have been running nonstop for a few years without any problems of this sort.
The cells are connected only through a central M.H. robot that is interfaced through RIO to both cells.
The cells are connected to Robot controllers through RIO and to a WinME Panelview.

I did a search but found nothing similer to this.
Any thoughts?
 
ScottTheEngineer said:
We have 2 robot welding cells in the rear of our plant that have just started getting Watchdog timeout faults on the SLC 5/05 CPU's.

"0022: The User Watchdog scan time has been exceeded. In the processor under the Data Files S2 - Status, Scan Times, the following is labeled:
Maximum = the highest scan time recorded, I believe this only resets if you download a new program x1, not sure though it might reset when you go from pro to run.

Average = the average scan time recorded x1

Watchdog = the limit that is set to trigger the error x10"

These cells have been running nonstop for a few years without any problems of this sort.
The cells are connected only through a central M.H. robot that is interfaced through RIO to both cells.
The cells are connected to Robot controllers through RIO and to a WinME Panelview.

I did a search but found nothing similer to this.
Any thoughts?

How often are the timeouts occuring? Do the timeouts occur while the cells are running, or also also when the cells are not running.

The fact that the code has been running a few years out almost certainly rules out a programming issue, unless there is something that was 'lurking in dark' all these years. Does the code have any conditional calls and any loops?

It is most likely a hardware issue, and I would start with replacing the RIO scanner as the M0/M1 file associated with RIO card affect scan time.

If you can't find out what is causing the problem, find out what is NOT causing the problem.

Ian
 
We found the problem. One of my fellow associates didn't like the way a portion of the program was runnning so he disabled part of it. The part he disabled was required to jump the scan out of a indirect addressing loop.

Therefore whenever a program fault of a certain type occured the processor would get stuck in the loop until it crashed.
 
ScottTheEngineer said:
We found the problem. One of my fellow associates didn't like the way a portion of the program was runnning so he disabled part of it. The part he disabled was required to jump the scan out of a indirect addressing loop.

Therefore whenever a program fault of a certain type occured the processor would get stuck in the loop until it crashed.

Okay, that part answers it, so the code was NOT untouched for years. Its like when my guys go to a site and the process crashes after they leave and I tell them...

"of course it was working, all you done was go online, modify code, change wiring and other than that, nothing was done to make the PLC crash."

Ian
 

Similar Topics

I have a SLC5/05 on Ethernet messaging to a SLC5/04 with a NetENI. So far all messages are good, but I have a few things running in the 5/04 that...
Replies
10
Views
4,426
Have a system with a main plc 5/40E on an isolated network with 5 slc's, 1 other plc 5/40E and about 8 mmi's running a VB application for mmi's...
Replies
1
Views
2,000
We are trying to come up with a program that will watch the communication between SLC and RsView; when communication is lost, an e-stop rung will...
Replies
0
Views
2,208
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
81
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
93
Back
Top Bottom