PV 600 RS232(485) to pc / Flexlogic

bradal

Member
Join Date
May 2006
Location
edmonton
Posts
156
Hello All,

I am trying to connect my laptop to a PV 600 part number
2711-T6C5L1. I have a NET-AIC module, Flexlogic PLC and the PIC driver installed.

Right now I am trying to connect the PC-PV. I have looked through manuals for the AIC and the PV. What cables/AIC combination do I need to connect the PV to Computer. Do I even need the AIC?

And if you could help me out for the connection to the PLC after I have downloaded the application to the PV that would be great.

Thank you all very much
 
You have a PV with DH485 protocol. From PC to PV you need a straight thru cable. See PDF below. You will need to configure the 1747-PIC/AIC+ driver in RSLinx to communicate with the PV. You need a real serial port to use this driver. I'm not familiar with FLexLogix controllers, so no help there from me.
 

Similar Topics

Hello,:) This is my scenario the ethenet of the slc is connected and the rs232 port is to be connected to the panelview. will the panelview...
Replies
1
Views
4,575
Hello all, I just got back to work and of course there is more to do than one person can realistically be expected to take on, so I was hoping...
Replies
2
Views
2,557
Hello, I have a set of three tanks with their own trio of Hardy 6600 series load cells. Two of them have no issues with where they are at and...
Replies
3
Views
145
Can anyone recommend a flexible 600-volt shielded ethernet patch cable? I have used them from Allen Bradley / Panduit before and they are too...
Replies
0
Views
102
Hi all, Im stuck trying to support a client with Motorola ACE.. I was able to upload all of the other sites to STS but one. Im working remotely...
Replies
0
Views
112
Back
Top Bottom