SLC5/03 communication problems

itamak

Member
Join Date
Aug 2007
Location
harare
Posts
1
Good people,

Please may you assist with a solution; When I try to download a program to a SLC 5/03 CPU, I get this message ‘No response from processor, Initdriver failed-code-1’ and below that ‘Current driver (AB_PIC_1) may not be running.’
 
The program that you loaded into RSlogix was last saved with a PIC driver.
Which driver are you using?
Make sure that RSLinx is running, and choose the driver that you want. The SLC5/03 can use PIC through a PIC or AIC, or DF1 to the serial port.
 
If yiour connecting through a 1747-pic make sure your serial port is set right in RS linx if yuo have the connection the RS linx should show the node. If your using the 1747-cp3 througha standard USB adaptor you will want to set the SLC-cho/micrologix/panelview. error checking CRC protocal fukll duplex. If your using the 1747-UIC and connecting to the rs 485 port you want to use the 1770-kf3/1747-ke driver I can't recall the cable to go with it I beleive its the 1747-c13 cable
 

Similar Topics

I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,546
Hi! I'm newer to PLC stuff as it seems to come up at the worst possible times at work. We have an old SLC5-04 connected to a Panelview 900. Over...
Replies
8
Views
773
Hi, I'm trying to accomplish communication between an SLC5/05 PLC and a M580 P582040 using a NOC0301 card. I was wondering if any of you have done...
Replies
1
Views
1,093
Dear All, I wanna get the data from ind331 indicator(Mettler toledo) to SLC 5/05 CPU via Ethernet Ip using EEM instruction. The CPU=1747-L553...
Replies
2
Views
2,152
Hi, I want to communicate slc5/03 cpu with Delta tp04 hmi through rs232 port. I tried through 1747cp3 cable directly but can not communicate...
Replies
0
Views
930
Back
Top Bottom