I had a strange problem with an old 5/15 that has been running untouched for years today that I have never seen.

PLC had a major fault in the middle of the night. Unfortunately my counterpart got to it before I did this morning and cleared the fault without looking at it. o_O

He couldn't get the machine to run so he called me. With the program in remote run I looked at the input data table and every input in the entire table was 1 even though the inputs weren't on. If you changed one of them from a 1 to a 0 it would reset it back to 1.

I went through all the error bits and couldn't find anything. Cycled the power and the same thing happenned.

Downloaded the program into it, same thing. Cycled power again and and logix told me that the program in the processor had changed do you want to upload. Now everything is fine and it's running normally.

This is a pretty simple little system, no RIO and all discrete I/O in the main rack. It talks DH+ to one other 5/40.

Has anyone seen this before or have a clue what might of happened?
 
I'd first disconnect the DH+ connection and try again. If it works, someone on the DH+ is messing things up.

But, what you describe sure sounds like a bad rack ('chassis') to me. The ONLY problem I ever had with 1771- stuff was a bad rack. So, (even though its a pain), change out the chassis, and see what happens.

Also, it may be that there's a connection problem brewing in the back of the IO modules. Turn ALL the power off, and pull the I/O cards one at a time, and use a high quality contact cleaner (no, not an eraser), and clean the edge connectors. If nothing else, simply removing and re-seating the IO cards may clear the problem.

Good luck, and let us know how you fix everything.
 
jdbrandt said:
...it may be that there's a connection problem brewing in the back of the IO modules. Turn ALL the power off, and pull the I/O cards one at a time, and use a high quality contact cleaner...and clean the edge connectors.

That was my same thought when I read the OP - hopefully its on the right track


(no, not an eraser)
I admit a good contact cleaner is better, but a good hard eraser has been a valuable tool over the years that has solved many mysterious problems.
 
I think in most cases the eraser is better. I know enough chemistry to realilze that any solvent that can un-oxidize a corroded terminal could also damage some components, including my lungs, and leave residue in undesirable spots. With an eraser, you can control where the dry, unharmful residue falls.
 
allscott said:
. . .Downloaded the program into it, same thing. Cycled power again and and logix told me that the program in the processor had changed do you want to upload. . .

You will always be prompted to upload from a classic PLC5/15. it does not provide the checksum for RSLogix to guarantee an exact program match, so RSLogix will always ask you to upload when going online. This is normal.
 
Thanks guys. The system is running fine now, the next time it goes down for maintenance I will pull the cards out of the rack and clean everything.

I'll post back if I find anything or if it happens again.
 

Similar Topics

I have created a project in TIA Portal v16 Upd6 with S7-1200 (6ES7214-1AG40-0XB0) and WinCC Unified (PC station). The communication between the...
Replies
4
Views
145
Hi guys, I've come across a very odd problem that I can't figure out with testing communications failures and my 1756-L72 ControlLogix PLC with a...
Replies
4
Views
5,600
I was writing a value on V1000 and it was changing the state of X3 which is a 3 bit on the input module .. :| is there any linking with the...
Replies
6
Views
4,427
Hi! I have two Mitsubishi A1S plcs operating two identical machines, and the program driving the plcs is almost identical (only the I/O...
Replies
1
Views
3,227
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
22
Back
Top Bottom