Hi everybody,

Can any one tell me how can I communication S7-400 PLC with Siemens MM4 VFD? It is very important.I know S7 200 can communicate with MM4 via USS by using some standard instructions, but this time I need to read/write MM4 parameters via USS from S7 400 PLC.

Thanks in advace.
 
Hello Apel;

First, if you can use Profibus-DP with your drive and your CPU, you will find it much more easier to establish comms between the two. Here is a link to an earlier post on plcs.net regarding this issue:

http://www.plctalk.net/qanda/printthread.php?t=25739

If you must use USS, then look at the foolowing possibilities:
-Drives ES blocks for USS:
http://www2.sea.siemens.com/NR/rdonlyres/94907391-14BA-49EB-90E6-F928E9C68C87/0/DriveESShortStartupInstructions.pdf
-USS and Profibus-DP standards:
http://electronica.li2.uchile.cl/CNC/Masterdrives%20%20MC/5.4.1%20DPV1%20Documentation/Dpv1-b%20-%20Acyclic%20Parameter%20Exchange%20-%20Profibus%20DP.pdf

You will need a serial CP on the S7-400 rack (CP441-2) to establish comms over USS protocol.
Hope this helps,
Daniel Chartier
 
dchartier said:
You will need a serial CP on the S7-400 rack (CP441-2) to establish comms over USS protocol.
A much less expensive alternative is an ET200S 1SI module with USS protocol (6ES7 138-4DF11-0AB0). Of course, you need to use ET200S.
Still, I agree that to use Profibus is overall the simplest and possibly even the cheapest too. The Profibus module for the Micromaster is surprisingly cheap.
 
Hi Jesper,

Thanks.I have setup S7-400 system with CP.I am trying using USS only. I undarstand that Profibus is better solution, but when system is already installed I cant change it to Profibus..is not it?
 
Wow, so you have already gotten the CP441 + USS loadable driver !
What did that cost you ?

I think that USS with an S7-200 and a MM4 is smart because an S7-200 supports USS directly on its serial ports, and the MM4 has USS on its onboard terminal strip. At least thats how I understand it. Thus you dont have to purchase anything extra to establish comms between an S7-200 and an MM4.
However, you will find that with S7-300 and S7-400, everything is focused on Profibus. I guess that a CP441 + loadable driver costs more than several S7-200 PLCs !
 

Similar Topics

Dear Friends; We have a BOBST 1228 flexo printing machine having Siemens S7-300 PLC (6ES7 318-3EL01-0AB0) and Lenze 9300 and 9400 drives. The...
Replies
3
Views
2,304
Hello, I'm used to using Allen Bradley RIO options for putting filed IO out in the field and running my safety back to it. Of course I have to...
Replies
5
Views
2,837
Dear Team, I need to increase the maximum speed of my drive upto 60 HZ. and sadly im stuck with some parameter. Below parameters are already...
Replies
5
Views
3,254
Hi, we have a Siemens ET 200S FC 6sl3244-0sa00-1AA0 that need to be replaced, I wonder how I should do to go online on this unit. I have tried...
Replies
3
Views
2,592
Hi guys, here is the project i want to control a siemens sinamics G110 drive via USS telegram on 485 serial interface. What is done; 485 serial...
Replies
0
Views
1,392
Back
Top Bottom