Can anyone tell me the difference between program,operator and override modes with the PIDE instruction in RS Logix 5000, and when they are likely to be used?
 
AB has not been forthcoming with examples of how best to use this block--I have also been looking for some professional guidance in this matter.

Anyway, in the interim, I setup about 15 PIDE's on a CLogix chassis, replacing the same number of single-loop PID controllers. I ended up using my own configuration of their block--testing rigorously as I went for bugs. So far, so good.

To answer your question, pp 1-62 in AB's publication #1756-RM006D-EN-P states that the block can either be run by a software app. (presumably a computer program), or by Operator Interface. They are apparently giving us the ability to use a multi-layered control scheme, should we so choose to use it.

My scheme is run in Program mode with a "1" wired to the pin to keep the block in that mode at all times. I have had no issues using it this way--
 
Information on the PIDE function block and how it works. Includes information on using it in Cascade and Ratio Control applications. This is a two part document which covers the majority of functions incorporated in the PIDE block.
Catalog Number: 1756 Generic
DocFullNum: G9057916


answerbase id is 21894 for 2 zip files 5/14/2002 .. seems to be pretty forthcoming.
 
Thanks for the replies, in the time since posting I have browsed the white paper that william martin mentioned. The document is useful in that it explains what the functions do, but not when one would use them.
 
Trust me, I have all of the AB technotes and articles pertaining to this block, and they DO NOT go into any further detail beyond the two out-of-the-can examples you mentioned.

Further, there is no mention of what happens to the block when uploading/downloading, such as A/M mode, valve position and SP changes that occur.

The current info available is lacking and less seasoned programmers can ill afford trial-by-fire methods of integration.

I disagree with your conclusion.
 

Similar Topics

There is a chilled water cooling loop in our process cooling a roller. It has been about impossible to tune. this is in a tertiary loop. From the...
Replies
6
Views
3,222
Does anyone have expierence with PIDE control of an on/off output. I am converting a heat treat oven from temperature controllers to PLC based...
Replies
2
Views
1,423
We have an oven with 32 zones and a Controllogix L7 controls the oven and all the steam valves, plate heaters and T/C's come in over different...
Replies
13
Views
5,441
I have created a PIDE loop in control logix and am for some reason unable to get this loop to function in AUTO. the outputs that are set telling...
Replies
1
Views
2,631
I am using the PIDE function in version 16 of RsLogix 5000 for a job which I am in the process of testing. The problem I am seeing is with the...
Replies
7
Views
6,018
Back
Top Bottom