If I have an analog output coming from a meter via a BNC connector, do I use the shield as the common? The signal will be a +/- 3VDC. I would assume that I should not ground the shield in this instance. Is this correct?
 
Well BNC connector only has 2 connections shield and pin... so yep yer stuck using the shield as minus signal... and a 3 volt signal will go straight to ground so no grounding the shield.....too bad it isnt a tnc connector.
 
You should not ground the shield, if it is at a different potential from the equipment ground it is attached too.

Generally, the shield there, is refernced to chassis ground (except in at least one notable exception, ControlNet). Is the female BNC on the connected equipment isolated from it's mounting panel?
 

Similar Topics

Hi All, I am working on a small PLC system having Compact Logix LE33 PLC having only two IF4 card. Some of these channels are used for 4 - 20...
Replies
4
Views
1,156
Hello. I'm dealing with a 1769-IF4 module with the "OK" light OFF. Data is not updating in RSLogix5000 - no change when inputs are connected or...
Replies
4
Views
1,810
I need some help. I have a 1769-IF4 analog card that is hooked up to strain gages, the gages give a 4-20ma signal to the card. We had an...
Replies
9
Views
2,025
Dear members I believe I have the difference in the modules correct: 1769-IF4, has one converter handling all 4 input by turn 1769-IF4I, has a...
Replies
1
Views
2,388
I have installed 1769 IF4 analog input module in compact logix rack slot 3. I have an existing 1769 8 channel input card in slot 2 already...
Replies
2
Views
2,430
Back
Top Bottom